What are the code references for obstructions greater than 4 feet wide (ductwork) but located only 18" from the floor?
We have a mechanical room with several large ducts 5 ft wide x 3 ft tall. The ducts are only 18" from the bottom of the duct to the finished floor. Additionally, there is a second level of a similar-sized duct that is mounted above, which leaves a 12" space between the top of the lower duct and the bottom of the upper duct. Would we be required to install two levels of shadow protection under each duct, or are there provisions that allow sprinklers to be omitted if there is limited space below the duct? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Anthony Crispo
8/5/2024 07:52:38 am
NFPA13- 19&22ed 9.5.5.3.1.5
Reply
Glenn Berger
8/5/2024 08:12:11 am
Thanks for the reference. I wish that NFPA folks would provide a commentary why they chose that number (24 inches in this case).
Reply
Anthony
8/5/2024 09:45:45 am
I would guess 2' is too short for storage as a bent/squatting person usually wouldn't have their face at 2' A.F.F. so it'd be unlikely to have a box of stuff. Similar to occupancy in an emergency/fire, it's an unlikely area to hide. Also NFPA generally choses round numbers for ease of use.
Dan Wilder
8/5/2024 01:54:44 pm
Took a bit but:
Peter Howard
8/5/2024 08:22:33 am
From NFPA 13 (2016 edition):
Reply
Franck
8/5/2024 09:21:39 am
This is a quite unusual situation.
Reply
Jack G
8/6/2024 12:27:38 am
I agree with Anthony . 24 inches the requirement. Believe me after a few years and maintenance is done there wil be filters, motors, and boxed replacement parts everywhere.