|
I am working on a mixed-occupancy project using NFPA 13 (2013 Edition). The ground floor is commercial space and Levels 2-6 are residential.
The residential areas use residential-type sprinklers with two hydraulic calculations; one in a suite on Level 6 (4 sprinklers), and the other in the Level 6 Corridor. How many sprinklers should be included in the corridor calculation? Section 11.2.3.4.2 suggests it should be 7 sprinklers since they form a line down the corridor. Section 11.3.1.1 suggests that it should only be 4 sprinklers since they are residential-type. What section is correct here? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Peter Howard
4/13/2022 06:37:06 am
I'd go with four because they're residential type sprinklers and you're in a residential occupancy, just a common corridor.
Reply
Anthony
4/13/2022 08:14:54 am
7 if you're using QR sprinklers.
Reply
RayJ
4/13/2022 08:20:35 am
I would calc both and have done a building similar to this.
Reply
JI
4/13/2022 08:26:39 am
I'd be more inclined to go with 11.2.3.3.6 for most corridors assuming the corridor allows the room design method is allowed to be used (which is 5 sprinklers, residential sprinklers while spaced like extended coverage sprinklers, are not extended coverage sprinklers and do not fall under the 75 linear feet rule). I don't think you can use 11.3.1.1 for corridors since it is not a dwelling units as per 11.3.1.5. Curious to see if others use the 4 head calculation in the corridors since you are allowed to use residential heads as per 8.4.5.1.
Reply
James Phifer
4/13/2022 08:27:33 am
The appendix (2016 ed) figure A.11.3.1.1(a) detail (b) shows an example of a calculated area in the corrido with 4 residential sprinkler heads.
Reply
Casey Milhorn
4/13/2022 08:30:30 am
Four, if the corridor is connected to at least one residential unit. If you have common areas, unconnected corridors, etc... then you will use SSP QR sprinklers and calc accordingly. I don't always do a corridor calc when using residential heads because many times your corridor heads are fed from a larger main down the middle (1-1/4" to 2") and your units are fed with 1". It would be a rare exception to need the corridor calc (for example, unit heads are spaced at 14x14, and corridor heads are at 20x20. Or if using a different K factor for units than for corridors). Even if you factor in a little more delta flow at the corridor heads, its not near enough to outweigh the friction loss through the 1" in the units.
Reply
EYount
4/13/2022 08:30:47 am
If it’s residential sprinklers it would be 4 and if it’s QR it would be 5.
Reply
Scott Stoltenberg Jr
4/13/2022 08:37:35 am
I would have to say it is 5 based on 11.2.3.3.6 or 11.2.3.3.7.
Reply
Jack G
4/13/2022 08:48:48 am
I personally, because residential systems have unprotected areas/ rooms, would use the 7 sprinkler design.
Reply
Alex
4/13/2022 10:29:31 am
Hi Jack, curious on your design approach here. Would you add additional heads if the doors don't align with your spacing? Seems like it could increase the number of heads real quick!
Reply
Todd E Wyatt
4/13/2022 10:34:46 am
I recommend you have the Architect-of-Record (or AHJ) verify the exact "residential" occupancy(s) per the applicable IBC ...
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
