I am designing a community tornado storm shelter and per ICC 500, Section 309.1, any penetration of the shelter envelope by a liquid line is to be provided with an automatic shutoff.
How is this being achieved with sprinkler pipe penetration? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
10/29/2024 06:41:23 am
I could be entirely wrong, but my best guess is with an automatic shutoff valve listed for fire protection. Here are the two I found:
Reply
Nic J
10/29/2024 08:10:09 am
Reading the second paragraph in section 309.1 it states "hazardous gas and liquid.." I read it as the intent is to provide an automatic shut off for hazardous materials possibly entering the space. I've worked on the design for a couple of storm shelters and never had to install automatic shutoffs on sprinkler or standard plumbing lines.
Reply
Glenn Berger
10/29/2024 08:16:39 am
I am with Nic J on this one. Shut-off valves for hazardous materials, not for fire suppression systems.
Reply
Chris Nelson
10/29/2024 09:56:29 am
Im just a lowly new englander, but arent tornado shelters in the ground? Could water flooding from the sprinkler be considered a hazardous liquid?
Reply
Jack G
10/29/2024 10:55:35 am
I agree that the auto shut off is for hazardous gas and liquids.
Reply
Ricardo Gonzales Jr
12/2/2024 02:25:49 pm
Water is hazardous when the occupants can't get out. Food for thought.