Do you have to protect the whole attic that has smoke partitions with fire sprinklers if only one area has gas-fueled equipment in it?
Can you just protect the one area that has the fuel-fired equipment in it? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Brett
5/11/2026 06:38:55 am
Which NFPA standard applies? 13D, 13R, and 13 all have different requirements. From the picture it looks like this could be a residential application.
Reply
Jennifer
5/11/2026 02:02:24 pm
NFPA 13R, apologize for that.
Reply
Brett
5/11/2026 02:35:47 pm
13R says to provide at least one quick response sprinkler above the equipment. For the 2019 edition see sections 7.4.2 and 6.6.6.1. The intent of 13R is not to sprinkler the entire attic unless the building code requires otherwise.
Jesse
5/11/2026 08:10:40 am
Is this NFPA 13, 13D, or 13R?
Reply
Jennifer Cornett
5/11/2026 02:02:36 pm
NFPA 13R
Reply
Todd E Wyatt
5/11/2026 08:14:36 am
What is the scoping Code ... IBC-YYYY?
Reply
Glenn Berger
5/11/2026 08:32:43 am
As others have mentioned - Need to know which codes are applicable.
Reply
Jack G
5/11/2026 05:04:20 pm
Regardless— I protect all fuel fired heater spaces.
Reply
James Art
5/13/2026 01:24:06 pm
Just curious.
Reply