In NFPA 13 (2025), where does it show what AREA discharge is needed for the Rack Storage tables?
I'm looking at Table 21.4.1.2.1 for Class II, up to 15", 8-foot aisles, and it says a density of 0.22 for ordinary temperature sprinklers, but what AREA? It happens that this is inside a cooler (44 degrees F), which is why I am not looking at the high-temperature values. Any assistance appreciated. Anything else I should know? In CA, we are just starting to use the 2025 Edition, so it is new to me! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
1/26/2026 07:14:12 am
As to changes, both AFSA and NSFA have courses, webinars, and cheat sheets available.
Reply
franck
1/26/2026 08:09:14 am
Unless otherwise indicated in the tables, it is 2000 sq ft for class I to IV. For rack and pile storage tables.
Reply
Jesse
1/26/2026 08:23:38 am
2000 sq. ft. And Dan brings up a good comment regarding temperature. And there are numerous K=11.2 dry pendent sprinklers with intermediate and high temperature ratings, I use them frequently for cold storage. The Meyer Fire Tool Kit has an awesome sprinkler database!
Reply