If a light hazard room is 13 feet x 13 feet, and a k5.6 pendent sprinkler is located seven feet from two of the walls, what is the sprinkler area used for hydraulic calculations?
In short, to determine the minimum flow from a sprinkler in multiplying the area by the required density, is the actual area of the room used (13'-0" x 13'-0" = 169 sqft) or is it computed the same as the maximum area of coverage for a sprinkler by doubling the furthest distance from adjacent walls [(7'-0" x 2) x (7'-0" x 2) = 196 sqft)]? For a room like this with a K5.6 sprinkler k-factor, it would make a difference between delivering 19.6 gpm to a room (0.1 gpm/sqft x 196 sqft) and 16.9 gpm to a room (0.1 gpm/sqft x 169 sqft). Posted anonymously for discussion. Discuss This | Submit a Question | Subscribe
13 Comments
Chad
4/30/2019 08:52:34 am
I am a little confused on you distances. If the sprinkler is 7'-2" off one wall and 6'-6" off the other. Your area coverage for that head would be 14'-4" x 13'-0"= 186.33 so your gpm for that head would be 18.6
Reply
MODERATOR
4/30/2019 08:54:54 am
Sorry, I didn't do a good job of vetting that. I believe the intent was 7'-0" off both walls with a room that is 13'-0" x 13'-0". I'll update the question to match.
Reply
Chad
4/30/2019 09:40:15 am
If it's 7' off two walls, your area coverage would be 14' x 14' regardless if the room is 13' x 13'. You take the largest distance of spacing.
Reply
Erick
4/30/2019 10:21:29 am
8.6.2.1.2 The requirements of 8.6.2.1.1 shall not apply in a small room as defined in 3.3.17; the protection area of coverage for each sprinkler in the small room shall be the area of the room divided by the number of sprinklers in the room.
Reply
Chad
4/30/2019 10:43:48 am
Completely forgot about the small room rule. Good Stuff!
Patrick
4/30/2019 10:18:04 am
Because this is light hazard, you can apply NFPA 13 8.6.2.1.2, which states: the requirements of 8.6.2.1.1 do not apply to small rooms as defined by 3.3.22; and 8.6.2.1.2.1 states: the protection area of coverage for each sprinkler in a small room is the area of the room divided by the number of sprinklers protecting it.
Reply
Dan Wilder
4/30/2019 10:27:05 am
Is it considered a small room? Look at 13-16' - 8.6.2.1.2.1
Reply
PETE
4/30/2019 11:21:26 am
I think the small room rule is being misinterpreted here. It is intended to eliminate the necessity for a second sprinkler (in the single sprinkler example) for a room that is slightly larger than the maximum spacing requirement on a single dimension. Look at the appendix.
Reply
Franck
4/30/2019 11:45:24 am
The small room rule could be considered, as indicated above.
Reply
Bruce Seiler
4/30/2019 02:46:32 pm
The small room could be used in this case to calculated the square footage for the sprinkler head as stated above, however I agree with Franck, this is not going to save you much in calculations and could open the final design up to scrutiny. I have had AHJ's question the square footage of sprinklers when calculating the actual square foot protected. Say we didn't have a sprinkler head in the design area that was over 168 sf, they would say no sprinkler head in the system could be spaced over 168 sf unless another calculation was completed to prove that area worked with the higher demand of that sprinkler. I don't run into this that often, but it is something that could come up. Also, if this sprinkler head isn't the most remote sprinkler, it could be moot point. In the end, it would come down to is it saving you a pipe size or not. Good question though. The theory behind what to figure in calculations is always a good debate within my staff.
Reply
WES
5/1/2019 08:11:39 am
Well said Bruce. I agree that tightly designing the system would cause restrictions for future modifications or potentially open up different remote areas depending upon how much area is attributed to each sprinkler.
Reply
Mike
4/30/2019 07:31:54 pm
Having a large end head pressure is not advisable for 196 Sq ft. It will jack up the flow of the 2nd head especially using 1“ pipe on maximum spaced heads resulting in higher overflow. Even though this is a small room, it may create an alternative "hydraulically" most remote area unless it is fire resistive per NFPA for Room Design Method.
Reply
Herminigildo Sia
11/9/2021 09:48:17 pm
is it considerable for my designed area of 840 sq. meters and my choose of coverage area is 12 and the spacing is 12.4 meters
Reply