Are sprinklers required within an enclosed (conditioned) pedestrian walkway that connects two fully sprinklered buildings?
The walkway is 80 feet (25+ meters) wide and 26 feet (8 meters) above a roadway where vehicle loading and unloading may occur (temporarily parked vehicles are not considered storage). Is the walkway considered an exterior projection from each connecting building, and since it is an occupied space, will sprinklers be required under the walkway structure? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
10/30/2025 06:01:04 am
From NFPA 13 (2016 edition)
Reply
Glenn Berger
10/30/2025 08:10:00 am
Depending on the applicable codes:
Reply
Todd E Wyatt
10/30/2025 08:21:07 am
IBC-2024 Section 3104 Pedestrian Walkways
Reply
Anthony
10/30/2025 08:19:37 am
A.8.15.7.2 Vehicles that are temporarily parked are not considered storage. Areas located at drive-in bank windows or porte-cocheres at hotels and motels normally do not require sprinklers where there is no occupancy above, where the area is entirely constructed of noncombustible or limited-combustible materials or fire retardant–treated lumber, and where the area is not the only means of egress. However, areas under exterior ceilings where the building is sprinklered should be protected due to the occupancy above.
Reply
Jack G
10/30/2025 08:42:23 am
Egress---sounds like its in the egress route.
Reply
franck
10/30/2025 10:58:11 am
I will give my point of view from a pure insurance perspective (which could be similar to AHJ).
Reply
Chad
10/30/2025 01:59:46 pm
100% agree with Franck's assessment from an AHJ perspective.
Reply
Donnie
10/31/2025 06:24:33 am
Why not sprinkle throughout since the space is a conditioned space instead of looking for exceptions and assuming both buildings are sprinkled? I’m sure some small furniture will end up in the space or even trash cans. If it is required egress, I would suggest sprinkler protection since you cannot exit from a protected area into an unprotected or less protected area.
Reply
Anthony
10/31/2025 07:55:34 am
I wouldn't consider trash cans and or a lounge chair to change a room's designation from non combustible to combustible. Those are incidental items to the occupancy not a core feature of the occupancy. I would compare this for example to the volume of material needed to change from LH to OH1/OH2 say from an office to a mercantile low pile storage arrangement.
Reply
Todd E Wyatt
10/31/2025 08:19:30 am
The AHJ has a say as to what contents are permitted in a Pedestrian Walkway (PW) :
Reply