What are the applicable requirements for speaker placement in high-rise Group R-2 buildings equipped with fire alarm or emergency voice/alarm communication systems, specifically regarding speakers inside dwelling or sleeping units?
What practices have you been applying or enforcing in these areas? Industry feedback suggests inconsistent approaches: some designs include speakers within bedrooms and living rooms, while others install speakers only in the corridors and rely on in-unit smoke-detector sounder bases for occupant notification, expecting residents to move into the corridor to hear prerecorded or live voice messages. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Todd E Wyatt
12/16/2025 08:33:20 am
The Code defines a SLEEPING UNIT as “rooms or spaces for one or more persons, includes PERMANENT PROVISIONS FOR SLEEPING.” The Code does not define “SLEEPING ROOMS” but most AHJs apply the prior definition to both bedrooms as well as areas that could be used for sleeping, like a couch area in a Living Room.
Reply
Todd E Wyatt
12/16/2025 08:33:52 am
REFERENCES
Reply
chad
12/16/2025 08:38:01 am
Strictly speaking you need voice in the units, its black and white in the IBC. Some cities take the approach you describe. I don't see that way as bad, just not ideal.
Reply
Joe
12/16/2025 09:01:36 am
I have seen AHJ accept no speaker inside the bedroom provided you comply with the intelligibility requirement with the bedroom door close.
Reply
Dylan Denmyer
12/16/2025 08:42:15 am
On residential high-rise buildings, I will layout:
Reply
Ricardo Gonzales
12/16/2025 08:49:32 am
NFPA 72's expanded definition of a sleeping room includes where a couch is. If you can fall asleep while watching TV in a room not called a bedroom, then it's a sleeping room. NFPA 72 A.3.3.258 & A29.8.1.1(1). It's in the 'A' appendix but I've found more AHJs using this than the standard 'Bedroom' definition.
Reply
Chris Nelson
12/17/2025 01:14:53 pm
2019 NFPA 72 18.4.11
Reply