|
There is a great debate in my office whether or not we are required to protect to the back of lower/upper cabinets.
NFPA 13 9.2.9.3 (2022) states that we need to cover the area below the cabinets to the back wall. Seems pretty straightforward to me, but someone in my office states that we only sprinkler floor space, without providing any code reference. Do we protect to the wall, or the face of the cabinet where only floor area is exposed? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
5/1/2026 08:15:43 am
I would refer to 9.5.1.3 as to intent of where sprinkler protection is measured from.
Reply
Dan Wilder
5/1/2026 09:10:43 am
Got submit happy...
Reply
Glenn Berger
5/1/2026 08:34:59 am
Agree with Dan.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
