Small Mechanical Closet a Plenum/Small Space?

4/8/2025

8 Comments

 
Question regarding a mechanical closet and/or plenum. We have what I'll call a mechanical closet because it houses an electric AC/heating unit for an apartment using NFPA 13.

The sprinkler designer/contractor is calling it a plenum/small space and is omitting sprinklers. The plans do not show any sprinkler coverage.

Is this closet a plenum or small enough space to omit sprinkler protection? Is there code justification for this?


Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
8 Comments
Pete H
4/8/2025 06:36:51 am

You're in 13 and you have mechanical equipment in the mechanical closet (it's an accessible space with mechanical equipment).

I'm leaning on: You have to protect it.

I can't verify if that specific HVAC unit is fuel-fired or not, but that would only make me say "you have to protect it more."

Reply
Dan Wilder
4/8/2025 07:58:56 am

This would really need to be seen on a floorplan with clarification on if this is a fuel fired piece of equipment of not (looks to be all electric but to confirm), size of the door access, and construction type around the unit.

The unit itself (assuming a non-fuel fired unit), when placed in an attic of non-combustible construction would not trigger the need for sprinklers. The fact it's ground level only changes the access to be easier, thus the ability of storage could occur within the unit space. If the plenum is of "tight" construction as to not allow storage around the unit and the access is only for a filter change out and electrical service panel access, I could see a good argument to omit sprinklers. This all assumes that the wall construction is non-combustible as well.

Also, if the ductwork out of the unit completely takes up the space above the unit as to not allow a sprinkler could be used as another possible reason to omit protection.

Reply
Glenn Berger
4/8/2025 08:18:55 am

Not enough information provided to render to proper response.

In addition to the comments made by others:

What is the size of this mechanical closet?

Is there any other equipment provided in this space?

Reply
Jesse
4/8/2025 08:30:06 am

Full 13 design has me leaning to protect the space. Isd this eequipment combustion fuel fired or electric?

Reply
Jack G
4/8/2025 10:31:56 am

From the label, it appears the appliance is a heat pump. It has a compressor and blower motor. It’s 200-230 volt single phase.
The amps distress me a little bit.
I d like to look at the size of the wire hooked up to it. It indicates I believe when I blow up the pic 14.6 to 16.2 amps.
When determining the wire size it’s always you determine the breaker size. It’s 1.25 times the amps for the breaker size . In this case
14.6 x 1.25 is 18.25 or a 20 amp breaker and a 12-3 wire.
For 16.2 amps x 1.25 is 20.2 which by code should be a 10-3 wire ( exceeds 20 so go to next size )
NFPA 13 system indicate the space should be protected with sprinklers. I ve seen reports In my 55 years in fire protection where fires in electric supplied appliances had fires start in hot water heaters, heat appliances At connections, blower motors , capacitors ( for start up— usually installed instead of a soft starter switch like we d do on an air compressor) My neighbors house had a big fire in his home at the hot water heater while he was taking a shower alone in his house. Ended up undersized wire. And this stuff does get by inspectors.,
I question the wire size as to expect the documents to show a 12-3 wire size which is maxed out for the breaker size. That plus the distance the wire has to run could cause high heat, the breaker tripping a lot under high load, and if the owner locks the breaker in ( little wires attached to the breaker)in on that hot summer day….an electrical fire. I would not be as concerned with 10-3 wire for an electrical fire but the wire size is important in this case and “ go cheap “ is the option usually followed, but as I stated a full NFPA 13 system would require it to be protected.
Thank you for providing the appliances electrical
Label.

Reply
Michael Ruda
4/8/2025 10:38:56 am

Ultimately that decision would be up to the Authority Having Jurisdiction.

Reply
Todd E Wyatt
4/8/2025 11:34:30 pm


If the scoping Code (e.g. IBC-2024) requires an automatic sprinkler system (ASPS ... see 903.2 Where Required) based on the building's Occupancy Classification (see 903.2.1 - 903.2.10), or per Specific Building Areas and Hazards (see 903.2.11), or during construction (see 903.2.12), then ASPS protection is required "throughout".

The scoping Code includes select rooms/areas/spaces where the ASPS is exempted (see 903.3.1.1.1 Exempt Locations) but this "mechanical closet" is not specifically listed.

If this equipment is located in an "attic" and the building is protected by a NFPA 13R ASPS, there are some exemptions (903.3.1.2.3) that may be applicable. Otherwise, a NFPA 13 ASPS is limited to those exemptions listed in 903.3.1.1.1.

Reply
Todd E Wyatt
4/8/2025 11:35:45 pm

REFERENCES
IBC-2024
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.3.1 Standards
903.3.1.1 NFPA 13 Sprinkler Systems
903.3.1.1.1 EXEMPT LOCATIONS
Automatic sprinklers shall not be required in the following rooms or areas where such rooms or areas are protected with an approved automatic fire detection system in accordance with Section 907.2 that will respond to visible or invisible particles of combustion. Sprinklers shall not be omitted from a room merely because it is damp, of fire-resistance-rated construction or contains ELECTRICAL EQUIPMENT.
1. A room or space where sprinklers constitute a serious life or fire hazard because of the nature of the contents, where approved by the fire code official.
2. Generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.
3. ROOMS OR AREAS THAT ARE OF NONCOMBUSTIBLE CONSTRUCTION WITH WHOLLY NONCOMBUSTIBLE CONTENTS.
4. Fire service access elevator machine rooms and machinery spaces.
5. Machine rooms, machinery spaces, control rooms and control spaces associated with occupant evacuation elevators designed in accordance with Section 3008.
903.3.1.1.2 Bathrooms
903.3.1.1.3 Lithium-Ion or Lithium Metal Batteries

903.3.1.2 NFPA 13R Sprinkler Systems
903.3.1.2.3 Attics
Attic protection shall be provided as follows:
1. Attics that are used or intended for living purposes or storage shall be protected by an automatic sprinkler system.
2. Where fuel-fired equipment is installed in an unsprinklered attic, not fewer than one quick-response intermediate temperature sprinkler shall be installed above the equipment.
3. Where located in a building of Type III, Type IV or Type V construction designed in accordance with Section 510.2 or 510.4, attics not required by Item 1 to have sprinklers shall comply with one of the following if the roof assembly is located more than 55 feet (16 764 mm) above the lowest level of fire department vehicle access needed to meet the provisions in Section 503.
3.1. Provide automatic sprinkler system protection.
3.2. Construct the attic using noncombustible materials.
3.3. Construct the attic using fire-retardant-treated wood complying with Section 2303.2.
3.4. Fill the attic with noncombustible insulation.
4. The height of the roof assembly shall be determined by measuring the distance from the lowest required fire vehicle access road surface adjacent to the building to the eave of the highest pitched roof, the intersection of the highest roof to the exterior wall, or the top of the highest parapet, whichever yields the greatest distance. For the purpose of this measurement, required fire vehicle access roads shall include only those roads that are necessary for compliance with Section 503 of the International Fire Code.
Group R-4, Condition 2 occupancy attics not required by Item 1 to have sprinklers shall comply with one of the following:
4.1. Provide automatic sprinkler system protection.
4.2. Provide a heat detection system throughout the attic that is arranged to activate the building fire alarm system.
4.3. Construct the attic using noncombustible materials.
4.4. Construct the attic using fire-retardant-treated wood complying with Section 2303.2.
4.5. Fill the attic with noncombustible insulation.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT