I have a small 580 sq. ft. attic, fed by a dry system, next to a wet system in a retail outlet mall. They are 2 separate systems at the valve assembly. The ceiling for the dry system is 10-ft higher than the wet system.
Would a phantom flow be required here? If so, would it be added at the valve assembly, where they meet? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Peter Howard
3/21/2025 06:44:51 am
Yes.
Reply
Anthony
3/21/2025 08:00:36 am
It's always worth an ask not to do phantom flow. An e-mail to the AHJ costs like 35min, writing a strong e-mail with a couple screen grabs showing the area scope.
Reply
Mike Morey
3/21/2025 08:12:02 am
I always suggest evaluating whether or not room design method is applicable/legal. Only density/area method calcs are subject to phantom flow. If the areas are adequately separated I call out room design method and do not add the phantom flow.
Reply
JI
3/21/2025 08:30:04 am
If the wet system and the dry system are protecting the same floor area. Yes.
Reply
Jesse
3/21/2025 08:50:07 am
By the letter of the code, yes phantom flow is required. However, as its only applicable for density / area calcs, I wonder if there is the case to make for room-design method.
Reply
D
3/21/2025 09:40:22 am
Adding to what others have said- yes, I believe technically by the letter of the code it would be required. I am unaware of any real way around this other than the room design method or getting the AHJ to approve without. Most AHJ's I've worked with do not require this even if you don't call out the room design method. I'd be willing to wager most of them have not even heard of it.
Reply
Jack G
3/21/2025 05:02:13 pm
I ve been calculating sprinkler systems for 60 years. I’ve seen and done all the iterations and changes.
Reply
Jack G
3/21/2025 05:10:47 pm
I ve done hand calcs, peaked grids, ( anyone ever use a slide rule on calculations) TI-52 programs, done them on a telephone modem to a mainframe ibm-9300.
Reply