For a single-family home with a 6 in 12 sloped ceiling (roof) that is a combustible wood structure.
Does this need a 1,950 sqft calculation due to the slope, or just two sprinklers as NFPA 13D requires? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
7/30/2024 06:47:39 am
Has the architect already called this out as a 13D job in the code sheet?
Reply
Ivan Humberson
7/30/2024 08:20:13 am
Also, bear in mind that the language in NFPA 13D states that the design has to be the two sprinklers that require the greatest demand, NOT the two most remote sprinklers. Typically, with a sloped ceiling compartment, the greatest demand from two sprinklers in the compartment will be the highest, most remote sprinkler, and the lowest sprinkler nearest the water supply.
Reply
Casey Milhorn
7/30/2024 08:54:03 am
Pete H nailed it. Just make sure you aren't referring to NFPA 13 unless specifically directed by 13D. They are 2 completely different standards and 13D does a fairly good job of pointing you to 13 for certain situations.
Reply
Jesse
7/30/2024 10:35:44 am
What Pete said...
Reply
danefre
7/30/2024 11:19:50 am
Calculation will be per NFPA 13D. If you do not meet the criteria for height (24ft peak) then you need AHJ approval for a more conservative design. We've had success calculating 4 heads instead of 2 for sloped ceilings that exceed 24ft in height. A-frame, log cabins etc. are all designed that way.
Reply
Jack G
7/30/2024 12:09:41 pm
If under IBC code, there are at least a dozen conditions where 13d cannot be used, height increases, area increases egress increases , types of construction and more.