I have an IT room with FM-200 under the raised floor and a pre-action sprinkler system at the ceiling. Contractors are replacing CRAC units.
Should the CRAC units be connected to the suppression system to shutdown upon activation of the FM200 system? I have done 2 days of research with no answer. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
7/8/2025 06:36:05 am
https://www.meyerfire.com/daily/shutdown-crac-unit-for-clean-agent-discharge
Reply
Mark Harris
7/8/2025 08:25:12 am
Halocarbon clean agents are heavier than air so if unit is shut down the agent will leak and cause a descending interface (minimum design concentration level height will drop). This is considered as part of the door fan test and ceiling height verses top of protected equipment.
Reply
Glenn Berger
7/8/2025 08:31:47 am
The comment does not mention if power to the Data Equipment will be terminated upon fire suppression system activation. The comment also does not mention if the CRAC Unit only serves that one room. I have come across some clients who will require a "centralized" room for CRAC Units to serve multiple ITE spaces.
Reply
Anthony
7/8/2025 08:59:40 am
The are should be air seals at the time of clean agent discharge for the appreciate amount of time per NFPA 2001.
Reply
Franck
7/8/2025 09:53:29 am
That’s a complex question as the FM200 is apparently only under the raised floor (preaction sprinkler for the room itself) and the concentration has been calculated on this quite limited volume only.