Hi, I am asking a follow up question to the post, "What's Required to be in a Shop Drawing?"
Having completed working drawings for contractors in NYC in the past, everything on the NFPA 13 Chapter 23 list was required. I've even been asked to resubmit for lack of a graphic scale, "jerks!" Ever since then, it has been my opinion that the Working drawings should be able to be used as a standalone reference, meaning no other document retrieval should be required to completely understand the system layout and duplicate the calculations. I'm currently reviewing shop drawings prepared by an extremely reputable FP engineering firm, and many of the required items from the checklist are missing. Of the applicable items, the explanation is that the information such as compass point, building sections, water service line, etc., are part of the CD set and therefore not required. Pipe elevations are included in the calcs, so they are not required on the drawings. Fire sprinkler and major valve manufacturer and model numbers are included in the product data, which, by the way, was not submitted by the contractor with the drawings and calcs as specified and is not this engineer's fault. Having said that, when sealing working drawings for contractors, we would require that information on the drawings so that it was clear to other entities that the equipment being provided matched the calcs. They also said that cut lengths are not required because these are not fabrication drawings. They said the quantity of sprinklers doesn't matter because there is only 1 riser and they are all the same temperature. I have complete confidence in this engineer, I'm just wanting to check myself for future reviews. For the record, I'm of the opinion that this should be returned and resubmitted with the product data. Other than that, things like graphic scales, compass points and other minor missing line items I would say minor correction to be included in the Owner's Record Copy. I don't know how many times I've asked for FP information for a building and the only information available is the working drawing. Am I wrong in thinking it should be as easy as possible to duplicate the calcs with only the working drawing available? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Pete H
4/11/2025 06:29:10 am
In regards to calcs, I would say absolutely not wrong. That would be why NFPA 13 has all those requirements under "working drawings".
Reply
Glenn Berger
4/11/2025 08:10:46 am
The NFPA requirement (and most client's requirements) have not matured over time. With electronic submissions and electronic recordkeeping, adjustments need to be addressed.
Reply
Casey Milhorn
4/11/2025 08:39:49 am
Funny enough, I just had lunch with a young FPE yesterday. Recently he had a project where full shop drawings were required to be submitted by the EOR during initial submittal of the full plans and specs. This is not the norm for most areas across the US. Luckily, this FPE started his career with a fire sprinkler contractor and knew how to develop shop drawings that meet the NFPA 13 criteria. I'm personally not a fan of FPEs or PEs developing shop drawings, unless they have someone like this on their staff. Even then, the EOR isn't always looking for the safest and most economical method of layout and installation, which can lead to a full redesign by the awarded fire sprinkler contractor (if allowed). It can also lead to lots of friction and change orders between GC and awarded fire sprinkler sub. To answer your question, I would say if your drawings will be the actual installation shop drawings, and no other shop drawings will be developed and submitted, then yes, all of these items should be on there. If these drawings are serving more as "design intent" drawings, then no, the NFPA 13 checklist shouldn't apply. But enough information should be on there to meet your jurisdictions standard of care. If that standard of care happens to require full NFPA 13, shop drawing compliance, then you will have to provide everything stated. My two cents anyway.
Reply
David D. Dexter, PE
5/26/2025 11:37:07 am
Just a comment, the EOR (Engineer Of Record) holds the ethical, moral and legal liability for the design. The EOR may be a PE or an FPE, but their design is what has been approved in the permit process. It is not up to anyone else to change or alter that design without the EOR's approval. To do so is basically committing a fraud against the Owner.
Reply
Mike Morey
4/11/2025 09:01:05 am
Working at (and reviewing all outbound submissions for) a large contractor I can say that we absolutely require every item on the NFPA checklist. When I review a drawing that is intended to be submitted I expect it to tell a complete story. Down to the design criteria, head types etc. I always try and put my "lowest common denominator" hat on and expect not to have to know ANYTHING about sprinklers to be taught how our designer came up with this design. We cite tables, modifiers etc as well. We have a very low rate of rejections, obviously a lot of the plans are being rubber stamped out there anyway, but doing it right cuts down on mistakes on our end, and cuts down on questions/rejections on the other end and the extra time designing is made up for by the lower instance of errors and rejections. I will say for standard valves that have an NFPA friction loss we normally don't submit or call out a model #. that was the only thing I noted in the OP I might not agree with.
Reply
Jose Figueroa
4/11/2025 10:49:54 am
This question is extremely important to me. Coming from an older generation, I remember that detailed working drawings or standalone drawings were essential for performing hydraulic calculations using a slide rule.
Reply
Brett
4/11/2025 03:27:49 pm
Jose,
Reply
danefre
4/11/2025 01:50:51 pm
Coming from the contracting world, I realize that a lot of overzealous reviewers don't understand the impact that their "Revise and Resubmit" has to the project.
Reply
Jack G
4/11/2025 05:37:13 pm
I ve been arguing for 50 years, there is too much on the drawings. Light fixtures, tiles, pipe centers/ cuts, elevations notes yada,yada.
Reply
Ft
4/13/2025 02:08:32 am
The industry has lost “common sense”
Reply
Jesse
4/13/2025 04:51:18 pm
I'm a couple days late to this party, but my 2-cents.....
Reply
Todd E Wyatt
4/14/2025 02:41:39 am
Contract Documents (CD) or Construction Documents (CD) included both DRAWINGS (DWG) and SPECIFICATIONS (SPECs).
Reply
Ricardo Gonzales Jr
4/14/2025 10:14:57 am
I'm in agreement that the drawings with equipment data sheets should stand alone. As a former AHJ, (Tech prior & FPE) I expect the drawings to provide all the information needed to properly build and test the system. The drawings and calculations should match and indicate where there is elevation differences. NFPA 13 is a fantastic guide. The only assumption I've ever made with reviewing drawings is that the designer has already done the coordination with any lights or diffusers or other obstructions in the ceilings or high on the walls. The inspections will be proof of the pudding.