I'm designing a system that has multiple, narrow tenant spaces divided by 2-hour rated fire walls.
When using density/area method, the square root × 1.2 design area doesn't include enough space to satisfy the 1500 square foot requirement. In this case, would I extend the area further parallel along the branch lines, extend it along the main into the adjacent space, or call it good where it's at? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Glenn Berger
4/4/2025 08:18:13 am
With the use of fire walls, there is no requirement to extend the design area further.
Reply
Chris
4/4/2025 08:29:38 am
Glenn,
Reply
4/4/2025 08:44:53 am
I am a bit confused by your description of the building. Firewalls are not just fire-rated walls, they separate buildings from one another and they must remain standing should the building on either side collapse. There is no requirement for sprinklers to be designed for the neighboring building, so you would have a long narrow design area for your long narrow building.
Jesse
4/4/2025 08:31:57 am
If these are indeed fire walls, you could call the area a compartment and use the room design method.
Reply
Mike Bergen
4/9/2025 02:57:41 pm
There seems to be some confusion
Reply
Brian Gerdwagen FPE
4/4/2025 08:32:50 am
If the wall rating is equal to or more than the design duration, stop your remote area at the wall.
Reply
Matt
4/7/2025 11:43:03 am
Brian, this makes a lot of sense to me, but I'm not sure I've ever heard it before. Is this a rule of thumb or written in the standard somewhere?
Reply
Eric R
4/4/2025 08:37:51 am
I think there is quite a bit of "depends" here.
Reply
Jack G
4/4/2025 09:12:56 am
Fire walls. In order for the areas with firewalls to be considered separate buildings is for the walls to create parapits thru the roof like you see where owners limit areas between the parapits to less than 12000 sq.ft in lieu of protecting the B occupancy with fire sprinklers .
Reply
Dan Wilder
4/4/2025 10:12:36 am
This will be good because I have been apart of some very "passionate" discussions with other designers and AHJ's about this...
Reply
Casey Milhorn
4/4/2025 03:52:08 pm
No need, use the room design method, as others have stated. The 1.2 goes out the window. This sounds like a prime example of why the room design method was created. HOWEVER, if the owner, EOR, or architect feel like this area is likely to be modified/expanded in the future, be careful as the owner may end up with an inadequate system. I wouldn't skimp on the underground and riser, just in case modifications happen later. Mains and branch lines can be modified/upsized a lot cheaper than taps, underground mains, and risers....
Reply