We have a room that will be used to store clothes within a changing room. The facility is a place of worship.
The owner is planning on 4' wide by 8' long free-standing storage shelves. We just discovered that the unit top will be only 4" below the ceiling. The room was planned for light-hazard concealed sprinkler protection. So, would you consider this storage? Or would you look at the shelving unit as an obstruction? In retail, we would limit the height of the unit to be 18" below the ceiling. But I'm not sure how to protect this build. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Pete H
5/22/2025 06:29:09 am
You can't have storage and a deflector that close in NFPA 13 (2016).
Reply
Chad
5/22/2025 07:36:20 am
Its an obstruction if within 18" of ceiling (unless against wall) like pete said.
Reply
Dan Wilder
5/22/2025 08:22:52 am
This is really no different than a tall bookcase, a modular storage, or other floor mounted obstruction within a library. Provide protection around the units keeping both the 18" clear below (aisleways) and minimum 6' between SSP (no sprinklers above the shelving)
Reply
Glenn Berger
5/22/2025 08:26:25 am
You got some really good answers already.