MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Shared Fire Line Monitored by Only One Building?

3/26/2025

6 Comments

 
Before people say, "Ask the AHJ," I am him; he is me.

I have an applicant who has combined plots of land with a mid-rise and some detached townhouses. A shared fire line supplies the two structures, but only the mid-rise FACP monitors the supply tamper.

The townhouse FACP will not know if the water is off (except for the tampers at the risers within the townhouse).

The buildings are owned by the same ownership. They are arguing they are technically meeting IBC 2015 903.4 "Valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels, and temperatures, critical air pressures, and waterflow switches on all sprinkler systems shall be electrically supervised by a listed fire alarm control unit."

It is being monitored, but the fire marshal and I are of the opinion this doesn't provide monitoring for the townhouse and does not meet the intent of the code.

Does anyone have any thoughts on whether a shared line can be monitored by only one building that it serves?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
3/26/2025 08:12:49 am

If the alarms from this one FACP are being transmitted to constantly attended location then in my opinion that would be acceptable.

Reply
Dan Wilder
3/26/2025 08:57:14 am

Our AHJ's would not allow this as ownership can change to easily creating one property to be dependent on another for the water supply for connected properties. Their justification is that selling either property would not trigger a building and fire code review that would identify the shared service however trying to split a single parcel would, due to ROW and Utility requirements.

You could use 2021 IFC 507.1 for an "approved" water supply, but that would also lead to needing something that would not allow this setup.

If this is a private fire service PRIOR to the fire line split with that single valve controlling both, then you could use your adopted NFPA 24 and reference (this is 2025 section)
6.2.9 - All connections to private fire service mains for fire protection systems shall be arranged in accordance with one of the following so that they can be isolated.

Have multiple structures without an ability to individually isolate and monitor them could be a violation of this section.

If each building has dedicated fire alarm capabilities, why were the townhomes exempted from the monitoring point and can it be added? Could this be the easy solution vs expensive UG modifications?

Reply
J.H.
3/26/2025 09:57:03 am

What does your adopted Fire Code require? All valves are required to be supervised under the provisions of NFPA 1:13.3.1.8 Supervision, and also NFPA 24:6.7.2.

The Townhome supply control valves should be reporting to the Townhome FACP. Since this is a shared private fire line, all control valves upstream of the respective Points of Connection need to be supervised and report to the affected bldg's FACP.

If there is not a Townhome supply control valve, one needs to be installed in compliance with NFPA 24:6.2.9.
You haven't mentioned the FDC situation, but each bldg's. FDC must also be connected inside the respective supply control valves.

I recommend consulting with Planning & Zoning to see if there are any Land Development Code requirements to consider, since it sounds like these are separate parcels.

Reply
Chad
3/26/2025 10:39:36 am

“It is being monitored, but the fire marshal and I are of the opinion this doesn't provide monitoring for the townhouse and does not meet the intent of the code.”

I can see this going both ways, but since you said it does not meet the intent of the code what would in your mind? Depending on the distances between the common valve and the buildings. Potter makes a wireless device that could transmit it to Both buildings…. you would need one transmitter for each building, and virtually every single sprinkler supervisory/tamper switch has a DPDT output.

Reply
Jesse
3/26/2025 10:52:42 am

Agree with Glenn and Dan on this one. Yeah, the if the tamper transmits to a continuously attended location then no problem.

But Dan's comment about if part of the property were sold is a very real issue. But then, who owns the tampers and who is responsible for maintenance and testing???

I think I owuld make the townhomes monitor it as well

Reply
Jack G
3/26/2025 11:10:21 am

One service for 2 properties is not ideal but is allowed.
Shutting off 2 properties with 1 valve is not a good idea either..
IBC 903.3.1.5 restricts one service for 2 buildings ( except if approved by the AHJ—- there you go )
The restriction is there to ensure that a fire in one building does not compromise the water supply and fire protection to the other buildings connected to the same riser.
For 2 buildings connected to a single water supply, NFPA 72 requires each building has its own fire alarm system, ( each has its own FACU) and that they function as a single fire alarm system meaning they must be interconnected and share a common control panel.
The FACU in each building should have its own remote annunciators that display alarm conditions in the other buildings FACU locations and both systems should allow for resetting and silencing alarms from any panel.
72 .23.8.2.1, and 72.23.8.2.2.
Also MeyerFire 3/7/2023 discussion.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT