On a fire pump system that has a large PRV on it, should there be a test of just the fire pump, as in the fire pump annual test, and also separately a test with the pump through the PRV?
This would ensure that the reduced-pressure standpipe/ sprinklers work ( system acceptance ). Are these required to be separate tests, or can they be combined? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
6/19/2025 09:20:03 am
In short, ITM activities should be separate. System Acceptance Testing falls outside of NFPA 25 into the applicable NFPA so that too would be a separate test.
Reply
Jack G
6/19/2025 10:22:50 am
No, the PRV should not be tested during the flow of a fire pump test ( thru it ) ( fp test manifold after the prv) as the flow characteristics for the pump may hit pressures and flows that would damage the prv.
Reply
Glenn Berger
6/19/2025 10:24:23 am
Since the question used the word "should" - My response to that will be YES.
Reply