In order to use pipe and fittings, they need to be "listed for fire protection service."
Do fire pump sensing lines need to meet this listing? What about compressed air lines coming from the air compressor to the air maintenance device, do they need to meet this listing? What about air on the downstream side of the maintenance device? We're curious on different methods to install these components where some fittings & pipe combinations are listed and some aren't (such as copper pro-press for sensing lines). Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Glenn Berger
1/13/2026 08:59:27 am
Good question.
Reply
1/13/2026 09:26:37 am
Viega ProPress carries the FM1920 Approval which is for Pipe Couplings and Fittings for Above Ground Fire Protection Systems but you'll have to use B-88 copper tube. The fittings approved are detailed in the approval guide (2915 Coupling, 2916 Ell, 2926 45 Ell, 2918 Tee...)
Reply
Anthony
1/14/2026 07:31:35 am
List for FP use - no. Pipe doesn't need to be specifically listed for FP it needs to be in compliance with Table 7.3.1.1 Pipe or Tube Materials and Dimensions (NFAP 13-22)
Reply
Dan
1/14/2026 01:31:12 pm
A lot of contractors I see like to use copper on Pump Sensing lines. Since this equipment is in a Pump room (OH occupancy) this stuff needs to be brazed and not soldered. I don't think I've ever seen this stuff brazed.
Reply