Room Rating and Base Required for Fire Pump?

1/5/2021

9 Comments

 
A couple of questions about an electric vertical inline fire pump:

(1) Is it necessary to build a rated room around a fire pump that is located in a boiler room that is already 2-hour rated construction?

(2) Is it required to have a concrete base poured below a vertical fire pump if we can bolt the pipe flange stand to a concrete floor?

​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Craig link
1/5/2021 09:13:27 am

Yes, it is necessary to build a separate rated enclosure around the fire pump. Looking at the 2019 edition of NFPA 20, Section 4.14.1.1.5 specifically notes that rooms containing fire pumps are to be free from storage, equipment, and penetrations not essential to the operation of the pump related components. Boiler equipment is not essential to operation of the pump and therefore may not be located within a fire pump room. The only exception to this is domestic water distribution equipment as identified under Section 4.14.1.1.6.

You must also coordinate the location and access to a fire pump room with the fire department, as identified under Section 4.14.1.1.4. If the pump room is not directly accessible from the exterior of the building, Section 4.14.2.1.1 requires access to be made via a fire-resistant-rated corridor from an enclosed stairway or exterior exit. The fire resistance rating of those portions used to access the pump room shall not be less than that required for the fire pump room per Section 4.14.2.1.2. If the pump room is in the middle of a boiler room, this may be quite difficult to achieve and will require substantial coordination with the architect and other trades.

Reply
Glenn Berger
1/5/2021 09:21:08 am

Concur with Craig for the fire pump rating and what can be installed in the fire pump room.

Concerning the base, it is recommended to provide a base - there will be vibration and the floor will crack, which will eventually lead to fire pump failure.

Reply
Brian Gerdwagen FPE
1/5/2021 09:39:27 am

The answer for the rated room is good.
The recommendation for concrete base and grouting comes from the pump manufacturer. It is in the drawings they provide with the pump.

Reply
Todd E Wyatt
1/5/2021 11:06:57 am

SHORT ANSWER
Rooms containing fire pumps shall be separated from all other areas of the building with either a 2-Hour Fire Barrier (2FB) and/or 2-Hour Horizontal Assemblies (2HA) OR by 1FB/1HA in sprinklered buildings.

LONG ANSWER
NFPA 20 is a referenced standard but the scoping document would be the IBC/IFC. The scoping Codes identify which aspects of the referenced standard are required to be met.

In reviewing 2021 IBC Chapter 35 Reference Standards, this chapter references the 2019 NFPA 20. NFPA 20 is referenced in the following sections : 412.2.4.1, 913.1, 913.2, 913.2.1, and 913.5.

412.2.4.1 : Fire-resistance rating (FRR) of fire pump rooms for airport traffic control towers.

Section 913 Fire Pumps
913.1 Fire Pumps - installation per 913 & NFPA 20
913.2 Protection against interruption of service
913.2.1 Protection of FP rooms with 2-Hr Fire Barrier (2FB) ... Exception #1 permits a reduction to a 1-Hour Fire Barrier in buildings protected by an automatic sprinkler system in non-High-Rise buildings.
913.5 Acceptance Testing


Reply
Tony C
1/5/2021 11:20:38 am

I agree with Todd as the IBC/IFC would take precedence.

Additionally referenced in the NFPA 20 (2013 Edition) HB.

4.12.1.1.4 Except as permitted in 4.12.1.1.5, rooms containing fire pumps shall be free from storage, equipment, and penetrations not essential to the operation of the pump and related components.
HB Excerpt: It is the intent of the standard to prohibit the use of a fire pump for the purposes of storage. It is not the intent if the standard to prohibit the installation of other types of equipment such as domestic water distribution equipment as indicated in 4.12.1.1.5. No materials or equipment that add to the combustibility of the space should be placed in the fire pump room. This provision is intended to provide protection to equipment as well as operating personnel.
A. 4.12.1.1.4 Equipment that increases the fire hazard (such a boilers) and is not related to fire protection systems should not be in a fire pump room.
4.12.1.1.5 Equipment related to domestic water distribution shall be permitted to be located within the same room as the fire pump equipment.

Therefore, the pump shall be located separately from any combustion type processes (such as boilers, gas-fired water heaters, etc).

Reply
Franck
1/8/2021 10:00:34 am

Boilers represent an exposure to the fire pumps.
As indicated above, it would be acceptable if it was a room housing domestic water distribution, but in your case it should preferrably be fire separated (you need to access the fire pumps in case of fire event on your equipment... What if the fire occurs on your boilers?.

Reply
Rad link
9/16/2021 05:18:54 am

On similar topic if you can guide me, for fire pump rooms located in basement, accessed through a common corridor, is this arrangement accepted if we provided the required fire rating, is t ok to have other rooms access (like plantrooms, storages) through the same corridor coming from staircase to fire pump room door ?

Reply
Barrett
10/16/2024 04:05:49 pm

Can HVAC cooling equipment be located within the room? I wouldn't think that would add more combustibility than the pump. What about penetrations into the room for supply and return air? Are those penetrations allowed?

Reply
Ashim D
5/31/2025 02:31:17 am

What Should Be The Minimum Size Of a Fire Pump Room. with any Standard Required

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT