Can a residential sprinkler be used in a building using NFPA 13 in lieu of NFPA 13R?
We have a hotel where a residential sprinkler is proposed with 0.05 gpm/sqft density, but the building is under NFPA 13. I'm rejecting it under 13 for the low density (believe it should be 0.10 gpm/sqft), but residential is permitted under a 13 building, correct? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
sean
12/26/2025 08:16:03 am
residential use is permitted but there are other factors if you do residential per 13 or 13R.
Reply
Jack G
12/26/2025 09:33:57 am
MeyerFire has a cheat sheet, December 2024, that goes thru what Shawn mentions above . How you build it, determines which type system, 13, R, D, you have or can use.
Reply
Jack G
12/26/2025 03:42:29 pm
Agree that the res heads can be used. But check to see which density you should apply.
Reply
Curtis Tower
12/26/2025 03:53:31 pm
The use of a sprinkler head listed for residential use IS permitted in a NFPA 13 residential application. The density is per NFPA 13, i.e.j .10; however, you must flow 4 of the most demanding heads regardless of whether they are in the same compartment or not.
Reply
12/29/2025 11:07:17 am
With it being NFPA 13 you also need to confirm if the interstitial floor spaces are fully insulated.
Reply