Requirement for FDC to Connect to All Systems?

2/18/2025

11 Comments

 
Best Practice suggests that a single FDC supply all fire sprinkler systems in a building, so ​no matter which FDC the fire department pumps into, all of the systems would be supplemented.

Is there a requirement in any code (except local, village, state amendments, etc.) that requires a fire department connection to connect to all systems?

Or, can each system have its own FDC, provided it's properly labeled as to what system(s) are being pressurized by that particular FDC?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
2/18/2025 08:06:33 am

While it can be acceptable to have an FDC for individual portions of buildings (13-19 16.12.5.4 & 16.12.5.6 for example) based on sprinkler zoning, it is not advisable.

The reasoning (IMO) is that the responding trucks do not have knowledge of where the fire is occurring so waiting for that info to connect to an FDC can be very detrimental to the response efforts vs connecting one time and heading into where the red stuff is.

Also, if there are multiple locations for a fire, or multiple locations of hose valves that are independently fed by multiple FDC's, many agencies do not carry enough gear to accommodate a multi-attachment approach much less the possibility of needing additional pumper trucks for FDC locations not adjacent to each other. This also plays into the truck engineer who is trying to balance GPM and PSI requirements for their offensive & defensive crews.

Reply
Chad
2/18/2025 08:27:25 am

Dan is right all around… For the love of god do not do that without checking with the FD.

Without proper planning this could be a huge issue for the FD unless that’s their SOP

Reply
Bill
2/18/2025 08:32:40 am

In high-rise buildings it isn't unusual to have multiple FDC connections for a specific number of floors. the FDC's are normally grouped together with signage indicating low zone & high zone floors.

Reply
Glenn Berger
2/18/2025 08:38:06 am

I concur with the statements made by both Dan and Bill. There is one simple rule to follow here: Keep it simple!

Reply
J.H.
2/18/2025 08:53:22 am

Here are some excerpts and helpful handbook commentary on the subject:

NFPA 13:16.12.5.4 (2019 ed.)
For multiple systems, the fire department connection shall be connected between the supply control valves and the system control valves.

ENHANCED CONTENT
Collapse
An arrangement of multiple check valves introduces multiple failure points and increased maintenance requirements. Because NFPA 13 allows for unlimited numbers of zone valves, there is always a chance that a portion of the system cannot be supplied through the fire department connection because of a shut valve. There are no provisions in the standard that prohibit the installation of zone valves downstream of the fire department connections, even for single wet systems where the fire department connection is tapped immediately downstream of the system alarm check valve.”

AND--

“NFPA 13:16.12.5.6

Where a fire department connection services only a portion of a building, a sign shall be attached indicating the portions of the building served.

ENHANCED CONTENT
Collapse
Confusion can occur where there are multiple fire department connections or where the fire department connection serves only a portion of a building. If the fire department cannot determine which fire department connection to use, the proper connection — or any other connection — might not be used. On other occasions, the fire department might pump into a fire department connection that does not serve the fire area. To avoid those types of problems, NFPA 13 requires that where multiple systems exist the fire department connection serve all the sprinkler systems (see 16.12.5.4) and that connections that serve only a portion of the building be marked with the area they serve.”

In both of these cases, the text is referring to a single building with multiple protection zones, as shown in the figure below. It would be a nightmare to have individual FDCs for each riser inside a multi-zone building.
For illustration, see Figure A.16.12.5.5(b) Fire Department Connection to Underground Piping for Multiple Systems. I could not paste it here.

***NOTE:
If there are multiple sprinklered BUILDINGS (not multiple system zones within a building) , a separate FDC is required for each, as the FDC must be connected downstream of each building supply control valve. See Control valves, other than sprinkler system control valves, cannot be installed between the FDC and the sprinkler system. Check valves, other than FDC check valves, must be located between two control valves. See NFPA 24:6.1.1, NFPA 24:6.2.1.1, NFPA 24:6.2.2.1-2, and FIGURE A.5.9.3.2.1(b), NFPA 13: FIGURE A.16.12.5.5(b) for “Fire Department Connection to Underground Piping for Multiple Systems”.

Reply
Adam
2/18/2025 09:07:23 am

I'm not sure what the benefit would be to having the FDC not connected to all zones. If a sprinkler head or hose connection is not flowing in a zone, then it's connection to the shared FDC would not impact performance of the zone that is involved in the fire.

Reply
Jonathan W.
2/18/2025 09:32:21 am

Depending on your jurisdiction (state and local codes), IFC Section 905.4.2 requires in buildings where more than one standpipe is provided, the standpipes shall be interconnected in accordance with NFPA 14.

NFPA 14 section 9.4.1 requires standpipes installed in the same building or section of building to be interconnected. Section 9.4.1.1 permits the standpipes to not be interconnected where acceptable by the AHJ.

Best practice, and as others have mentioned, always have the conversation with the local FD and AHJ to determine their operational needs.

Reply
Jose Figueroa
2/18/2025 09:48:13 am

I refer to NFPA 14 & NFPA 1700
The latter shows:

7.4.4.3.4 Fire Department Connections.

Fire department connection is a method for the fire department to supply either a primary or a secondary water supply to standpipe systems or to supplement existing water supplies for fire sprinkler systems. Knowledge of the location and arrangement of fire department connections in advance of an emergency can facilitate more efficient and effective fire-fighting operations. The location can be visually identified on site by the appropriate signage or special lighting.

The question does not provide enough information. High-rise buildings or even large horizontal structures may require separate FDC and standpipe systems.

Reply
Jesse
2/18/2025 01:11:28 pm

Yeah Dan is right. And another vote for keep it simple.

Again though, we've all seen high-rises or large footprint buildings with multiple FDCs for various portions of the building. I've also done multiple FDC locations with each FDC tying into the same system.

Just make sure the AHJ is on board

Reply
Jeff Ayers
2/18/2025 03:51:01 pm

In the Multi Family world with IIIA structure wrapping a 6-story garage, we will have multiple FDC's.
Why?
Each area of units (not zones) have a 3-hour fire wall of separation. This creates its own "Building" (not zones) allowing "Phased Occupancy" of each of the 3 buildings.

For example, a 400 unit wrap project has 3 separate buildings, separated by 3-hour walls.

As each building is occupied, we have separate Fire Alarm (3 dialers and 3 FACP) and separate sprinkler for each building to stand alone, with separate FDC's.

Additionally, the garage has its own FDC.

Some jurisdictions do not allow phased occupancy, in which case we zone the FA and sprinkler in each building with a single FDC. But the garage always has its own FDC.

Sometimes the AHJ will accept a single FACP, allowing the other unoccupied buildings to show as trouble on the FA panel.

Reply
Jack G
2/18/2025 11:55:53 pm

As stated above , it’s not required, but why would you not want to tie them together with proper signage. It s just good fire protection. Each system would be checked off, so the fire fighter operating the pumper would have control no matter how many zones had fires.
Malls, big high schools, outlet stores, makes arriving to the scene and setting up less complicated.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT