Replacement Recommendation for NOVEC 1230?

2/26/2025

12 Comments

 
Where are we with the newest clean agents?

I'm running into an interesting scenario where the discussion of the phasing out by 3M of the NOVEC 1230 agent is coming up. I mentioned the competitors to NOVEC 1230 that we're aware of - FK-5-1-12 but they are interested in the next-gen stuff because they don't want to have to redo anything in the near future.

Does anyone have any experience with the Fluoro-K or any other newer, lesser used in the past but now have to look into agents?

I'm aware of Victaulic's Vortex and CO
₂ options, but I'm asking about chemical agents. I look forward to hearing your thoughts and experience.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Glenn Berger
2/26/2025 08:09:46 am

The folks that were behind 3M's Novec 1230 (NFPA 2001 generic name FK-5-1-12) are now working as Standard Fluids (https://standardfluids.com/). They are marketing SF-1230 as basically the same agent.

Reply
Christopher Nelson
2/26/2025 08:21:46 am

Still with the forever chemicals? They are promoting they arent affected by the AIM act for HFC phasedown but I wonder how true that is.

Reply
Josh Gilliam
2/26/2025 09:47:59 am

This is THE question for me. As a person who gives a crap in general, I am staying away from PFAs on my recommendatinos and specs.

JI
2/26/2025 08:21:38 am

Fluoro-K is essentially identical to Novec 1230. There are some small differences such as the concentration %, but is the same chemical. However, since it is the same chemical as Novec 1230, there might be some issues with PFAS law suits in the future.

I like oxy-reduct, and inert gases likes Nitrogen and Argon for ideas that use less complicated chemicals, but of course those have different design challenges as well. Nothing really beats water.

Reply
Joe
2/26/2025 08:47:54 am

Please check out the webpage below for more information.

https://www.fssa.net/pfas-resource-center#science

Reply
Joseph McElvaney
2/26/2025 08:32:47 am

Please remember that there is still a very large amount of recycled amount of FM 200 and Novec 1230 including Halon gas available. All these gases are still allowed to be used.

You should also be asking for certification of all gases (new and recycled gases) showing that its meets NFPA standards for quality requirements.

Reply
Josh Gilliam
2/26/2025 10:00:14 am

As an update to my post, on the particular project that trigger me posing this question to the forum, I went with IG-541 on that. Gas suppression only 1.2% heavier than air seemed like a good alternative for this scenario of protecting a very, very complex and costly $17M computer. The easiness in getting room integrity right was also attractive. The one negative on this so far is the number of cylinders required for a relatively small volume space. The 300 bar that's being changed up is a 72" x 14" cylinders. It has 12 of them and there's just not a ton of room for them.

Anyone have any previous experience with Argonite or IG-541 either one?

Reply
Joe
2/26/2025 10:20:03 am

One of the biggest issues is refill a 300-bar system. Where do you have to ship them to be refilled.

Reply
Josh Gilliam
2/26/2025 10:41:59 am

I've heard that the extremely high pressure on these is a little bit of an issue for refill, unfortunately. I can't remember where the JCI guy was saying they would be coming from now to save my life. I'm in the Southeast and it seems like there were only 2 places he named but I could be wrong. Turns out I've been wrong about 1 or 2 things in my lifetime.

Mark Harris
2/26/2025 12:50:32 pm

The AIM act financially stopped the FM200 HFC market in the United States. 3M did their last shipments of Novec 1230 in 2024 so United States has transitioned to generic FK-5-1-12 as the Novec 1230 replacement. There can be different manufacturers design requirements based on who manufactured the generic FK but in NFPA 2001 and FM Global data sheet 4-9 it just says FK-5-1-12 with no clarifications.

Have seen some end user sites say no PFAS products allowed but if they remove everything that may already have PFAS they would probably have to close the doors.

Ansul inergen has been around since the early 90's as a clean agent inert verses halocarbon alternative. In NFPA IG-541 for the inergen blended gas (52% nitrogen, 40% argon and 8% CO2). The CO2 increases respiration rate in the lower oxygen environment after a discharge. To the best of my knowledge inergen is the only agent that has been safety tested on humans.

Originally was 150 Bar (2,175 PSI) and later 200 Bar and then 300 Bar. Higher Bar means more agent in similar footprint so less cylinders and floor space. But still needs more floor space than any halocarbon agent (FM200, Ecaro, Novec, FK, halon). But the flow calcs are much more forgiving than halocarbon and while the 95% agent discharge time in calcs is longer the fire testing results are not significantly different. Cylinders can be much farther from the hazard (maybe mechanical room) verses halocarbon needing to be in or near the hazard for halocarbon systems.

Inert gases are natural products and do not generate hazardous HF acids at high temperatures.

Inert system discharges depending on room and location of nozzles to High Density Drive Server racks can damage the HDD drives. I can't speak to other manufacturers but Ansul does have an acoustic nozzle option for server room applications.

I have given many advantages for an inergen system but the economic reality is they are more expensive (more steel and containers to install) than an FK-5-1-12 system and as the conversation started need more floor space. The twelve cylinders in the referenced project may be one or two halocarbon cylinders.

Final comment keep in mind Flouro K is a Kidde brand name not the agent. The agent is FK-5-1-12. And for Ansul the Sapphire brand name applies to older Novec 1230 systems as well as the new FK systems.

Reply
Mark Harris
2/26/2025 01:01:58 pm

Forgot to address the comments about recharge. Josh has valid concern and inert manufacturers are working through it for third party authorized re-fillers and exchange programs. Most welding gas houses do not have capability or desire to deal with blended gases, 300 bar and the QC process from manufacturers and NFPA 2001.

Reply
Muhammad Jamal link
2/27/2025 03:28:52 am

NFPA2001 IG / inert gases system are the natural and best forever, rest all man-made chemicals which came in the market 1940 afterwards are harmful and useless to recommend to client or install same as Halon, FM200, Novec, FK etc all are man-made, client stakeholders are fed-up, and they don't want to have to redo anything in the near future. As being technical we shall recommend Inert gases under NFPA2001 at least they are related to natural. Further either first filling listed stations and refilling stations manufacturer has to established and they shall seriously work in these tasks.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT