MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Replace Old Sprinklers with Higher K-Factor?

2/12/2025

14 Comments

 
If the fire sprinklers for an entire area or building have to be replaced, such as if they are more than 50 years old, is there any problem or benefit (hydraulically) from increasing the replacement sprinklers to the next higher K-factor (e.g., K5.6 to K8.0 or K8.0 to K11.2), especially for production and storage areas?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Jesse
2/12/2025 08:06:59 am

Certainly a higher K-factor can be conducive to being able to provide a higher density, but the system would need to calculated with that K-factor sprinkler. Increasing the orifice size may lead to the system being hydraulically inadequate.

Reply
Allison Olsen
2/13/2025 09:47:14 am

I think the even more straight forward answer is, if the hydraulics worked, they would be limited to increasing to a K8.0, which have the same 1/2" NPT as the K5.6.

They could not upgrade to a K11.2, which are all 3/4" NPT.

To your point this system was hydraulically designed manually using the pipe schedule method, so the calcs would need to be done. Even then, without upgrades to the sprinklers its doubtful they could meet the current NFPA 13 requirements for manufacturing and storage without upgrades to the system, so then, what's the point?

Reply
Mark Fessenden
2/16/2025 06:36:52 am

JCI (Tyco) has an 11.2 k with a 1/2 NPT.

MICHAEL BRIAN MOREY
2/12/2025 08:09:46 am

Bigger isn't always better. Every increase in K factor increases the discharge rate of the head. While it lowers the pressure required for an individual head, it could very well increase the friction loss in the pipe. If the fire isn't controlled by the first few heads you may run out of water before you reach the entire design area. You absolutely shouldn't change K factors without a proper hydraulic analysis.

Reply
Eric R
2/12/2025 08:12:50 am

Besides the logistical issue of different thread size when going from 5.6k to higher, yes there is a significant issue with doing this without understanding the hydraulic implications of the change.

System piping sized to protect a specific hazard class will very likely not properly function over the full design area if the k-factor is increased. This is due to over-discharge from the larger orifice sizes that will compound as more heads open. You will quickly reach a point that the friction loss along the branch-lines causes your head pressures to drop below what is needed to supply the required discharge density.

I'll caveat this by saying that there are also plenty of system arrangements that can benefit from a change like this, but it will always be specific to the hazard class, head pressure required for the density, and the pipe layout/sizing.

Reply
Cordell Beache
2/12/2025 08:13:17 am

The system will need to be hydraulically calculated to ensure that the pipe sizes and water supply are adequate for the new K-Factor heads. There are sprinkler heads that can be used specifically for this type of system upgrade. They have 1/2" NPT with an 8.0K factor.

Reply
james
2/12/2025 08:17:52 am

Not only is the calculation requirements an issue but you have to take into consideration the coverage area per sprinkler. The higher K-Factors may require respacing to a lower coverage area.

Reply
Glenn Berger
2/12/2025 08:19:04 am

Yes - There can be problems utilizing higher k-factors than the original design required. See previous responses.

Yes - There can be benefits with utilizing higher k-factors than the original design provided.

Sprinkler systems that are older than 50 years most likely were not hydraulically designed (calculated) as these systems were installed in the 1970s.

Now is a good time to review the entire system. including supply, and provide updated recommendations to meet current standards.

Reply
Allison Olsen
2/13/2025 09:40:56 am

They would have been hydraulically calculated by hand using the principles of the old pipe schedule method.

Reply
Dan Wilder
2/12/2025 08:23:41 am

Change out of the sprinklers with a like-for-like k-factor is all that is required, anything more would require hydraulic analysis.

If you are being asked to perform a hydraulic analysis on the existing system and a larger K-Factor works, that may be an option provided the water supply & existing system works hydraulically, or the modifications needed fall within the owner's budget.

You may run into issues with a 5.6 to 8.0 K-Factor increase due to outlet size from 1/2" to 3/4" but allowed within NFPA 13 for existing systems only. There would not be an 11.2K option with a 1/2" thread.

Storage areas, especially high-piled, has changed so much that there are often large modifications needed. The city getting a chance to go back into a building to review the existing building also has its pit falls as they can now require alarm upgrades and egress modifications, address existing construction deficiencies, require racking permits, and generally create a lot more work than just the sprinkler upgrade so prepare your owner for that.

Reply
David Kendrick
2/12/2025 08:29:18 am

With review / consultation with a FPE I’d consider response time update. Inform / consult the insurance provider as well.
50 year old heads didn’t have a response time index like later products. Orifice is the same, hydraulic remote area should still be available.
Installing quick response could help.
Internal pipe condition could be reviewed during the process as well.

Reply
Chad
2/12/2025 08:31:17 am



I’m 100% behind everyone’s answers above and I’m glad the person did ask and not just changed to a higher K factor (Or I’d like to hope they didn’t?)

Reply
Franck
2/12/2025 01:24:23 pm

If there is no need for change of density, it might be problematic to change the k-factor for all above mentioned reasons.
In all cases, if you change the k-factor, a hydraulic calculation is mandatory to validate the change.

This being said, and especially for storage occupancy, it could be good to check if it is possible to change the k-factor and, in some cases, the temperature rating.
Larger k-factor means larger droplets for the same delivered density, thus more efficient to penetrate heat plumes from storage fires.
NFPA is now requiring to adapt the k-factor to the density with storage occupancy (and it was not the case 50 years ago).
Temperature rating change can also be beneficial for EH occupancy and storage occupancy when high temperature sprinklers are used instead of ordinary temperature.
The good news? Changing the temperature rating does not change the hydraulic calculation results.

Reply
sean
2/13/2025 10:24:27 am

Yes there is an issue.
you would need to recalculate

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT