I'm working on an existing 3-unit apartment building in Boston with an existing NFPA-13R system, which is being renovated.
Massachusetts allows 3-unit buildings to be designed per NFPA-13D. Can the renovations be treated as 13D, or does the system need to be kept as 13R? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Pete H
8/21/2026 06:00:56 am
I'd say stick with 13R.
Reply
chad
8/21/2026 07:44:46 am
yes, (assuming its staying 3 units) they can as per MA CMR 527. I don't recall the city's rules amending that. Its permissible to be a 13D, renovations of a 3 unit to a 3 unit does not change the sprinkler requirements.
Reply
Peter G
8/21/2026 08:19:37 am
Would they just be calculating the water for two heads versus four?
Reply
Glenn Berger
8/21/2026 08:11:11 am
Based upon the limited information provided, you can treat the revised system as NFPA 13D.
Reply
Jesse
8/21/2026 08:45:56 am
I can't speak to the local codes, but I personally wouldn't remodel to 13D. While similar, each standard has a different scope.
Reply
C
8/21/2026 08:58:17 am
What is the scope of work for the renovation? If you are maintaining the existing NFPA 13R system designed, I recommend staying with NFPA 13R and not mixing two different standards.
Reply
FP Engineer
8/21/2026 11:20:28 am
The interior work is pretty minimal, just relocating a few heads but the contractor is adding dry heads to exterior overhangs that wouldn't be required under 13D. Nothing wrong with that, just curious if it's necessary.
Reply
Jack G
8/21/2026 11:17:09 am
It depends on how the building was built. I d suggest reviewing meyer fire cheats heat 13--13r---13d to see if your project qualifies.
Reply
chad
8/21/2026 12:23:32 pm
MA allows 13D to apply on up to 3 family R occupancy only structures. Its not about D vs. R. Its D, period.
Reply
Jack G
8/21/2026 12:39:42 pm
Like I said above. How it was built depends on how its protected.
Reply
J Smith
8/21/2026 01:13:04 pm
It’s required to be maintained per the code it was built under unless they are bringing the entire building up to current code.
Reply