Reduce Hazard Classification Based on Testing?

4/2/2025

10 Comments

 
We are preparing drawings and hydraulic calculations for the storage of XLPE & XLEVA foam panels in an existing warehouse equipped with an Ordinary Hazard Group 2 (OH2) sprinkler system.

Based on NFPA 13, these products would fall under Group A plastics; however, independent testing indicates they do not exhibit the same ignition characteristics as standard polyethylene.
• XLPE (Cross-Linked Polyethylene) is chemically or physically cross-linked, enhancing its fire resistance.
• XLEVA (Cross-Linked Ethylene Vinyl Acetate) contains EVA, further modifying its properties. Third-party testing found that these materials did not have the same ignition characteristics as Group A Plastics.

Here are notes from the test report:
1. The specimen did not ignite.
2. The specimen ignited but self-extinguished prior to burning into the timing zone.
3. The material stopped burning before it burned for 60 seconds from the start of timing and did not burn more than 51 mm from the point where timing was started.
4. The test was discontinued at 5.0 minutes.

The customer plans to store 4' x 8' panels on wood pallets in a solid pile arrangement exceeding 5 feet in height.

Given that an OH2 system does not support Group A plastic storage above 5 feet, I'm looking for input on whether the test data could justify a reduced design density under NFPA 13 or if this scenario would require a performance-based design approach.

Does NFPA 13 allow adjustments based on fire testing like this?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Dan Wilder
4/2/2025 07:22:16 am

You can utilize Chapter 1 Section 1.5 but the testing looks to fall short. Yes, there was a 3rd party testing of the materials but was that in the same configuration as the proposed (storage) and per UL/ASTM/NFPA? While the material by itself or in combination with a construction method has shown those characteristics, was the testing completed in storage configurations expected? How about any sprinkler testing or equivalent materials that have had the same testing and density confirmed? Wrap all that up and submit to the AHJ for approval and you are good to go.

You can also find testing methods in the definitions of non-combustible, limited-combustible materials - ASTM E84/E136, NFPA 259, UL 723 to name a few referenced in Chapter 4.

1.5 Equivalency.
Nothing in this standard is intended to prevent the use of systems, methods, or devices of equivalent or superior quality, strength, fire resistance, effectiveness, durability, and safety over those prescribed by this standard.

1.5.1 Technical documentation shall be submitted to the authority having jurisdiction to demonstrate equivalency.

1.5.2 The system, method, or device shall be approved for the intended purpose by the authority having jurisdiction.

Reply
Pete H
4/2/2025 07:26:36 am

You can ask the AHJ that will be reviewing the plan and submit your test results that back up your theory to see what happens and if they'll accept you lowering the commodity classification. If you're doing this, I strongly suggest using the definitions of Class IV and Group A found in Chapter 3 of NFPA 13. I also suggest trying to link your test results to the test results NFPA 13 used for PET bottles or jars (empty containers), which in 2016 edition is a Class IV commodity, despite being made of Polyethylene plastic.

As for NFPA 13 themselves, you may need to appeal the committee that writes the updated editions with your test results. But that change wouldn't take effect for years at the earliest.

Reply
Joe
4/2/2025 08:10:23 am

So with all fire test report we should ask several questions,

What fire test was used?

Is this the correct fire test?

Was the material tested in a manner that is will be stored vs used?

Was this an approved test lab?

and i am sure others can add additional questions

Reply
Jack G
4/2/2025 08:24:04 am

Good Question: was the test used by a UL approved test lab or just 3 rd party.
Remember : Requirements in NFPA are minimal. So is it wise to minimize the standard?
How much would it cost you to replace the facility if you are wrong? Is your insurance company on board with this idea?
What are your qualifications as a design builder contractor, and a lot of insurance companies dot insure design builder contractors .
Nicet is not a PE license.

Reply
Jesse
4/2/2025 08:24:04 am

The testing, while done by a third party, was likely not done in the way the UL and others like the old Wassau may have done the test. Meaning in a specified storage array and in conditions that nmay be found in the actual storage arrangement you're protecting. Add packaging, pallets, etc, etc - you get the idea.

Some things, while taking a lot of time and heat energy to pyrolisize and begin the combustion process, burn much more effectively once started and the positive heat feedback loop begins.

I would recommend taking the fire test results to the AHJ, but they may not be receptive. You can also appeal to the 13 technical committee but this is a very long term approach and would take several years

Reply
Jon H
4/2/2025 08:25:39 am

The testing that was performed falls short of the requirements from NFPA 13 for determining commodity classifications. From the enhanced content of NFPA 13 (2022), section 20.3: "The likelihood of ignition is not considered in the commodity classifications". It also explains that the chemical heat of combustion and heat release rates are the factors considered for determining commodity classifications.

Reply
Jon N
4/2/2025 08:53:09 am

As a former AHJ, I am always skeptical of "3rd party tests" conducted by the product manufacturer. These are often not robust tests that place the product in conditions that mimic how it will be used or stored (similar to what others have mentioned).

This sounds like a glorified "match test" for flaming ignition. I would be looking for more of a full-scale test - like a room corner test - to see how the product behaves when it is exposed to radiant and convective heat from other burning materials. Remember, lots of burning plastics can pass these small-scale tests because the material itself no longer burns because it has melted and is currently a flammable or combustible liquid pool fire.

Reply
franck
4/2/2025 09:35:21 am

There is a difference between testing for fire behaviour in construction and classification for commodity class.
If you can demonstrate that the fire behavior is similar to group B or C plastic, then you can protect it as class IV or III. Otherwise it would be group A plastic.
It is not only the product itself that makes the classification but also the way it is stored. Corrugated cardboard is a class III if stored flat on pile, but becomes a class IV when stored as empty formed corrugated carboxes (just because of the quicker fire spread).

Reply
Chad
4/2/2025 10:37:38 am

I would like to directly answer the two questions posed.

No.

No.


No AHJ in there right mind is going to allow a loose interpretation or reduction based on those test results.... unless this was a well known organization such as UL. You are going to need to protect as class A or similar.

Most 3rd party "tests" are not performed properly or in alignment with the relevant standard. Oh sure they will reference a standard and follow it, just not the one that needs to be applied.

Reply
Jimmy Duke link
4/2/2025 11:34:27 am

Thank you for your feedback. I shared the question because I was also hesitant about relying on third-party testing but wanted to thoroughly evaluate all options before limiting the customer to a 5 ft storage height. I have recommended that the owner conduct a fire modeling study to assess their storage commodities and arrangement.

Thanks again for your input.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT