Recommend Antifreeze for Assisted Living Attic?

10/4/2024

10 Comments

 
I have a client who owns multiple assisted living facilities. It's residential construction with attic insulation on the roof trusses' bottom chord, and louvered gable ends with ridge vents.

They have existing wet pipe sprinkler systems in the attic and have experienced busted sprinkler lines in the past. They want to heat the attics to prevent this with electric heaters.

I have done the heat loss calculations and have determined the heating load would be more than their current electrical service can support. The only options I see available are heat trace, anti-freeze, or conversion to a dry system. Anti-freeze with
UL-listed anti-freeze was my first thought, but it looks like a backflow preventer would have to be added.

Does anyone have experience with this and/or have recommendations on how to address this?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
10/4/2024 07:09:21 am

You pretty much nailed the options I'd see.

Either the dry system addition (would not personally recommend full conversion, would recommend disconnecting your main feeding the attic from your wet system and reconnecting it to a new dry valve and keeping everything below the attic wet for maintenance) or the antifreeze should probably require installation of a backflow assembly if one is not present. In which case I'd just advise reviewing the existing system and calculations to make sure the additional loss from a backflow prevention device is something the system can absorb. Especially if the area would call for an rpz instead of a double check. Similarly remember that a dry system, especially an attic dry system is going to be significantly more hydraulically demanding than the existing wet (possibly residential) system.

If the system can take the hit and the compressor is not somewhere where residents would complain, I'd separate the attic and add the dry valve. If that's not an option, I'd go antifreeze.

If the system cannot take the hit of the backflow prevention device at all, let alone for a dry system calculation, now heat tracing seems a lot more fiscally practical.

Reply
Daryl Lovejoy
10/4/2024 10:35:57 am

Don't forget pipe will all have to be pitched on a dry system in accordance with NFPA 13 !

Reply
Dan Wilder
10/4/2024 07:53:29 am

Most AHJ's/Water purveyors require a Reduced Pressure Backflow when the water downstream is being introduced with any chemicals, FYI. This can push a tight calc into not being accepted with the additional PSI loss.

You did not include if the attic system is independent, or it feeds rooms below, material used (steel vs CPVC/Copper) and what NFPA you're expected to follow. Also, roof construction will need to be reviewed for area increases and decreases (Sloped 30%▲, QR used up to 40%▼, Dry system 30%▲), if it's flat there may be a combustible concealed option.

For a dry system, NFPA 13 has trip times that are much more lenient, pending the system size, for light hazard vs residential. Change in C-Factor of piping (standard air - If using N2 or other approved inhibitor you can keep the C-Factor of 120 in later editions), pipe sloping, aux drains, additional electrical for compressors, ability to drain drops, and return bends are all in the mix.

For Anti-Freeze the size of the system will also be a factor as 500 gallons is about the largest anti-freeze system you can have. The RPBF will also be a need along with filling and testing means.

Any chance to split the upper and lower systems?

The last couple times we have been approach for options; it was a several page proposal with pricing options showing pros & cons for each path.

Reply
Brett
10/4/2024 07:57:38 am

I concur with Pete's comment but I'd also like to add that the existing piping material could cause a wrinkle. If the piping in the attic is plastic and the intent is to reuse as much pipe as possible, then a dry system is out of the question and for heat trace you would need to make sure the cable is listed to protect plastic piping.

If this were new construction, typically the cheapest option is antifreeze with plastic piping. If you convert to dry or antifreeze know that you have to calc the system either way. Dry systems require a larger area and antifreeze systems (assuming this isn't a very small attic space) are required to be calculated with the Darcy-Weisbach equation. Darcy-Weisbach calcs in a cold area are typically more demanding than than a Hazen-Williams calc.

Also, anecdotally I've heard that heat trace simply isn't reliable in the long term and is a maintenance headache.

Reply
Jimmy
10/4/2024 08:50:09 am

Sounds like you need to upgrade the system completely.
Depending on the area involved height, roof pitch and square footage. There are newer heads designed for just for attic protection that can cover way more area than standard heads.

This means fewer heads and less piping,
It needs to be a dry system and maybe in zones using smaller dry valves for "zone protection" to keep the demand down.

Even if you need to replace all the piping the end cost result in coming years is the ultimate goal,... right?

Reply
Jonathan Griffin
10/4/2024 09:33:37 am

I would suspect that your Wet Pipe system serves the rooms/areas below the ceiling, not the Attic. The order of consideration here is:

1. Tent & insulate the piping within the Attic (Plastic or Steel)
2. Convert Plastic pipe system to Anti-freeze system
3. Convert Steel to Anti-freeze system
4. Convert to a steel Dry-pipe system; plan on making all Pendent drops Dry-barrel pendents

Good luck!

Reply
Glenn Berger
10/4/2024 09:44:42 am

You got the options stated correctly. I would recommend the heat trace system as long as power is deemed reliable.

Reply
Dave
10/4/2024 10:52:19 am

And for branch lines, using heat-tracing specifically listed for use on branch lines. (NFPA '19, #16.4.1.4.1)

Reply
Jack G
10/4/2024 07:17:44 pm

Dave and Glenn have the best options.
I would heat trace the pipe— wrap it with insulation to avoid excessive energy to keep pipe at 40 degrees F. Add blanket insulation where possible.
No rpz required. No recalculations, if the piping remains the same configuration, no breaking it up into 2 or more systems,,( heat traced wet system) .
I would also add unit heaters with digital probe into ( wet heat traced pipe in the attic) that would operate if the water in the system reaches 40 degrees, which it shouldn’t . This would make it fail safe if the power was more than reliable.
I did this on a military installations ( specified) for the same scenario as above.

Reply
Todd E Wyatt
10/7/2024 08:41:44 am

You may consider checking the attic exemptions for providing an automatic sprinkler system (ASPS) in a Group I-1 Assisted Living Facility per the scoping Code (e.g. IBC-2021) :

IBC-2021
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.3.1.2.3 Attics
Attic protection shall be provided as follows:
1. Attics that are used or intended for living purposes or storage shall be protected by an automatic sprinkler system.
2. Where fuel-fired equipment is installed in an unsprinklered attic, not fewer than one quick-response intermediate temperature sprinkler shall be installed above the equipment.
3. Where located in a building of Type III, Type IV or Type V construction designed in accordance with Section 510.2 or 510.4, attics not required by Item 1 to have sprinklers shall comply with ONE of the following IF the roof assembly is located more than 55 feet (16 764 mm) above the lowest level of fire department vehicle access needed to meet the provisions in Section 503.
1. Provide automatic sprinkler system protection.
2. Construct the attic using noncombustible materials.
3. Construct the attic using fire-retardant-treated wood complying with Section 2303.2.
4. FILL THE ATTIC WITH NONCOMBUSTIBLE INSULATION.
The height of the roof assembly shall be determined by measuring the distance from the lowest required fire vehicle access road surface adjacent to the building to the eave of the highest pitched roof, the intersection of the highest roof to the exterior wall, or the top of the highest parapet, whichever yields the greatest distance. For the purpose of this measurement, required fire vehicle access roads shall include only those roads that are necessary for compliance with Section 503 of the International Fire Code:
4. Group R-4, Condition 2 occupancy attics not required by Item 1 to have sprinklers shall comply with one of the following:
1. Provide automatic sprinkler system protection.
2. Provide a heat detection system throughout the attic that is arranged to activate the building fire alarm system.
3. Construct the attic using noncombustible materials.
4. Construct the attic using fire-retardant-treated wood complying with Section 2303.2.
5. Fill the attic with noncombustible insulation.

903.3.1.2.3-3(4) … FILL THE ATTIC WITH NONCOMBUSTIBLE INSULATION … is a solution I have seen approved by AHJs.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top June '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT