Reason Not to Omit Standpipes if Code Allows?

4/15/2026

8 Comments

 
I appreciate this community and thank you in advance. I'm new to the fire protection industry, having been in other building engineering disciplines for many years.

For multiple buildings on a campus using the IBC.

"IBC 905.3.2 Building Area Amendment In buildings exceeding 10,000 square feet (929 m2) in area per story, Class I automatic wet or manual wet standpipes shall be provided where any portion of the building's interior area is more than 200 feet (60,960 mm) of travel, vertically and horizontally, from the nearest point of fire department vehicle access.

Exceptions:
1. Buildings equipped throughout with automatic sprinkler systems installed in accordance with Section 903.3.1.1.
2. Group A-4, A-5, F-2, R-2, S-2 or U occupancies."


Is there any reason not to eliminate the standpipes if the height and occupancy thresholds aren't exceeded?

One of the buildings is a two-story, 60,000 SF building. The path of travel plans shows a 150+ foot range. Does this cause any concern?

I know the standpipes are to assist in manual firefighting ops, but is eliminating them increasing future risks to the occupants?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
4/15/2026 08:13:32 am

"Is there any reason not to eliminate the standpipes if the height and occupancy thresholds aren't exceeded?"

Generally, no. It's always going to be cheaper and easier to maintain something that never needed to be installed and wasn't installed.

But it's a world of infinite possibilities. So if you know that the building is going to be modified in the near future in a way would make standpipes required, it is easier to install those standpipes at initial construction.

As for the 150'-0" of travel distance, an AHJ might try to claim the path of travel plans are ending or starting at a point that he would disagree with (Start at corridor door instead of exit door), but that shouldn't be your problem unless you made that plan.

Reply
Todd E Wyatt
4/15/2026 08:38:11 am

The edition of the scoping Code (no amendments) for the cited 905.3.2 appears to be IBC-2021 (see below) with the localized amendment.

Per your question … Is there any reason NOT to eliminate the standpipes if the height and occupancy thresholds aren't exceeded? … my recommendation is to inform the Owner (the one who is paying for this Project) of the minimum Code requirements for standpipe “Required Installation” and your recommendation, as the Design Professional, of the proposed standpipe design that exceeds these minimum Code requirements.

As a Design Professional, it is our responsibility to provide a Code compliant design. The majority of what we design exceeds these Code minimums but we need to be cautious HOW FAR our designs exceed these Code minimums and how this will affect the cost of the Project. For instance, stairway clear widths are required to be 44-IN minimum but Architects will typically provide stairways that exceed this minimum width. A 48-IN wide stairway will cost more than a 44-IN wide stairway but Architects will typically not run this design decision by the Owner for approval.

If a Project does NOT require the installations of standpipes BUT the Design Professional feels their installation SHOULD be included, a discussion between the Owner and the Design Professional should occur. The Owner’s insurance company may offer a rebate with the installation of nonrequired standpipes that will pay for this standpipe installation after a few years. The Design Professional needs to be careful in adding nonrequired fire protection and life safety systems without the approval from the Owner.

Reply
Todd E Wyatt
4/15/2026 08:38:45 am

IBC-2021
Chapter 9 Fire Protection and Life Safety Systems
Section 905 Standpipe Systems

905.3 Required Installations
Standpipe systems shall be installed where required by Sections 905.3.1 through 905.3.8. Standpipe systems are allowed to be combined with automatic sprinkler systems.
Exception: Standpipe systems are not required in Group R-3 occupancies.
905.3.1 Height
Class III standpipe systems shall be installed throughout buildings where any of the following conditions exist:
1. Four or more stories are above or below grade plane.
2. The floor level of the highest story is located more than 30 feet (9144 mm) above the lowest level of fire department vehicle access.
3. The floor level of the lowest story is located more than 30 feet (9144 mm) below the highest level of fire department vehicle access.
Exceptions:
1. Class I standpipes are allowed in buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.
2. Class I standpipes are allowed in Group B and E occupancies.
3. Class I standpipes are allowed in parking garages.
4. Class I standpipes are allowed in basements equipped throughout with an automatic sprinkler system.
5. Class I standpipes are allowed in buildings where occupant-use hose lines will not be utilized by trained personnel or the fire department.
6. In determining the lowest level of fire department vehicle access, it shall not be required to consider either of the following:
a. Recessed loading docks for four vehicles or less.
b. Conditions where topography makes access from the fire department vehicle to the building impractical or impossible.

905.3.2 Group A
Class I automatic wet standpipes shall be provided in nonsprinklered Group A buildings having an occupant load exceeding 1,000 persons.
Exceptions:
1. Open-air-seating spaces without enclosed spaces.
2. Class I automatic dry and semiautomatic dry standpipes or manual wet standpipes are allowed in buildings that are not high-rise buildings.

905.3.3 Covered and Open Mall Buildings
905.3.4 Stages
905.3.5 Underground Buildings
905.3.6 Helistops and Heliports
905.3.7 Marinas and Boatyards
905.3.8 Landscaped Roofs

Reply
Anthony
4/15/2026 08:51:36 am

Adding to Tod's last paragraph

We need to examine these two questions:

What's the use case for this building?
Will the fire department actually use the standpipe.

I its a storage building with very few occupants I doubt the fire department is going in to the building to fight a fire. If its a hospital or building with probable people with mobility issues there's a case there. Also depends on how the AHJ plans to attack a fire for the building use case as you're putting in place a "nice to have" that is specifically for the fire department to be helped with manual fire fighting operations they should be part of the conversations. If the FD wont go into the building and use the standpipe then don't provide one.


I'd also add this is a MAJOR cost increase for dubious value with a high rise. All day a standpipe system is needed. For a single story building? eh, horizontal standpipes are hard to find in a cut up building with out pre fire planning and training.

Reply
Jesse
4/15/2026 10:04:21 am

I would absoslutely omit if I could. I'm in the AS business now, but I was a career firefighter for 19 years. That's well within the reach of a skid-load and eliminating SPs in a fully sprinklered building doesn't create any issues I can see.

Reply
Glenn Berger
4/15/2026 10:19:44 am

The question being asked today is: "Is there any reason not to eliminate the standpipes if the height and occupancy thresholds aren't exceeded?"

I am going to re-phrase the question to - Should one provide a system that is not required by code or other requirement?

Codes provide minimum requirements. Codes and standards cannot provide the requirement for every particular situation.

DOR/EOR need to provide systems that are proper for their specific project.

Providing systems that are truly not required cost money during construction and costs money to maintain.

In your specific case - to not install a standpipe system in one multi-story building with the other multi-story buildings having standpipes is a tough call. I probably will provide the standpipe system since the omission is the based upon just being below the maximum travel distance from the vehicle to the most remote point in a facility.

Reply
Jack G
4/15/2026 06:09:39 pm

Exceeding code with standpipes could be costly .
A manual wet standpipe could just add the standpipe and valves cost with the fire department providing the flow and pressure. Usually a hydrant is installed within 100 ft of the fdc for a M W SP.
A 100 psi NFPA 14 standpipe would most assuredly add a fire pump, if the water supply would support one.
If it does not then a tank or break tank would add to the costs.
Most owners only want what code requires.

Reply
Conrad
4/16/2026 01:51:35 pm

If the path of travel is close to the maximum allowed, consideration should be given to future improvements that modify or extend the path of travel. Examples include adding rows of racking/shelves, new rooms/walls, or large equipment.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT