Reason for Differences in Flow Test Results?

8/25/2026

13 Comments

 
We are working on a school project that needed a 1,000 gpm fire pump due to three standpipes.

We initially did a hydrant flow test and had a flow of 425 gpm with a static of 55 psi and residual of 50 psi when we started the design
. By the time it went out to bid and the contractor performed their own test,​ they flowed 354 gpm with a static of 55 and a residual of 50.

In the first test, we got 1215 gpm at 20 psi, and 1012 gpm in the second test. They went to turn on the pump and were only getting 368 gpm when the building inlet pressure was at 20 psi.

We re-did the flow test to see what changed so drastically and again got a static of 51 with residual of 46 at 375 gpm, which would give us 1004 gpm at 20 psi.

We have confirmed the two valves between the street and
the building are fully open, and we only have about 50 feet of 8” pipe, so the pressure drop to the building is negligible, especially at 368 gpm.

We are at a loss for what could be causing such a difference in pressure to the building and such a low flow.

​Has anyone ever run into an issue like this or have any suggestions of what else we could check out?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Pete H
8/25/2026 06:34:15 am

Is there any chance of a separate obstruction in the 8"? Or any other pipe damage?

Reply
Dan Wilder
8/25/2026 07:59:15 am

You have a theoretical 1000 GPM based on the assumption that the water supply remains consistent from ~400GPM through 1000 GPM....that is a long way to extrapolate data.

Were the tests performed at the same time of day? Is there any water data from the water utility for system configuration (pump stations on, normal usage charts through the day/night, height of any water tanks/towers in the area, commercial usage spikes, pump station operability)

My first thought is performing the test again and open enough outlets to get to 1000 GPM. And/or flush the underground with a flow meter to verify what the inlet side of the pump is actually getting.

Second, scope the underground line from the flange at the building backwards to verify no obstructions.

Beyond that, it becomes much more involved for a solution.

Reply
Anthony
8/25/2026 08:16:45 am

Why are the flow test results so low? Asking specifically why they're flowing such low volumes? Makes me think your feed taps out at ~1500gpm max. Do you even have fire flow high enough for this school? This is a serious infrastructure concern for any fire fighting in the area.

On the reason for why a flow test would be changing by 20%:

Seasonality

Time of day

Water supply construction

Closed valve in a looped system creating a dead end

Development taking water away from the system (literally had a water bottling plant open down the road from an ESFR project between install and initial design once upon a time)

City water supply engineering installing a PRV or flow restriction to protect a subdivision - had this happen in Texas.

Water main break that has not been recorded or identified.

Reply
CASEY MILHORN
8/25/2026 08:20:26 am

Dan nailed it. This is why it's always good practice to flow the actual amount needed during your test, and for a sustained period of time (not just for a few seconds). Open up as many outlets as needed to get that 1,000 gpm, and do it as close to the actual connection point as possible. We hade one awhile back that was a 2,000 gpm pump, and we could only get 1,600+/- gpm out of a couple of hydrants. The extrapolated gpm at 20 psi was 2,300 gpm... cutting it very close, but the EOR signed off on it. During commissioning, it was more like 2,000 gpm at 18 psi, and 150% was out of the question of course. No one likes a surprise water storage tank, not good for anyone. Sometimes as the sprinkler contractor, you have to "help" the EOR, just make sure you don't set yourself up to be liable by "helping".

Reply
Glenn Berger
8/25/2026 08:27:29 am

As others have said - "Time of day" is a major factor. You did not state the type of area where the project is located. In a city, you have times of day where there is major amounts of water being used.

Reply
Jeremy
8/25/2026 08:55:46 am

I've had a wedge ("paddle") fall of the stem of the building OS&Y before. This then restricted flow and we were finally able to find the issue. It was a tricky scenario at first though.

Reply
Brian Gerdwagen
8/25/2026 08:58:11 am

Is there a golf course, farm, or industrial plant nearby that may be using a bunch of water? If you're really curious, use a pressure logger on a hydrant nearby for a few days to check the static throughout the day for a week.

Reply
danefre
8/25/2026 10:23:42 am

This happened because the project was issued to the contractor without first verifying that the water supply could support 100%—let alone 150%—of the rated flow at 20 psi. That is not a valid flow test.

You never actually achieved 1,200 gpm or even 1,000 gpm—you assumed it based on 2 points on the graph.

Please follow NFPA 291—the requirements are there for a reason. The available water supply must be established through a proper flow test. The graph is only an extrapolation and should not be treated as proof of the available supply.

That being said, we've literally found a 2x4 stuck in the fire service before. I'm still not sure how it got there, but we pulled it out. There are a lot of factors and surprises that can affect the available flow.

Perform flow tests at locations farther upstream until you can isolate the problem segment of piping. Do them at the same time of the day!

On a separate note, is the school that large and tall that it needed automatic standpipes? Maybe try to prove a manual wet standpipe and then your max demand will be maybe a dry OH2 system and you can satisfy that with a 500gpm pump.

Reply
Jack G
8/25/2026 11:00:41 am

You have forgotten the most important rules.
Never extrapolate beyond the amount of water you flowed.
Always flow at least the amount of water you need .
Flowing additional hydrants to get the achieved flow, however I d
request a map of the water mains and fire hydrants showing the size and locations supplying your site.
While it’s true there could be an obstruction such as a fallen os& y wedge somewhere there also could be another possibility.
In areas with weak water supplies, the hydrants and mains could be sized to flow a maximum amount of water say maybe 400 gpm.
( city of Trenton NJ had 6 inch looped water mains in the city supplied by 8 inch mains sized somewhat like a deluge system where the pipe sizing controls the flow) some times this is for supplying say 400 gpm in 2 or 3 locations ( simultaneously) but only 400 gpm in one location.
If this is the case your location will only flow that maximum amount of water.
The water supplier can upgrade the pumps but would have to replace the water mains ( Trenton is doing) to get better results.
I would request a map showing the area water mains and the city supply to them.

Reply
Jack G
8/25/2026 11:06:50 am

Also if old cast iron water mains supplying your new service ( examine the coupon) the old mains could have sediment and or corrosion affecting its size ) . There is a chart in NFPA showing the c factor to use on the pipe based on its age.

Reply
chad
8/25/2026 11:10:45 am

Its time of day or some other variable affecting the results. Assuming all else equal, others suggestions are a good place to start troubleshooting.

Need the water dept involved as well. If variables are controlled, scoping the line is next.

Reply
Sean
8/26/2026 10:50:44 am

All good comments here. If still looking for additional direction to investigate, verify your pump arrangement. Do you have a double check on the suction side of your pump? Is it restricting flow into the pump? Even differences across backflow manufacturers can cause huge losses and obstructions. Do you have OS&Y's and gate valves on the suction side, or butterfly type?
What flow meter are you using on the pump? Is it rated for accurate readings at such low flows? It is 1000gpm flow meter right? Be sure you blead the air out of the tubes.
What equipment is being used to measure actual discharge flow from the test header? Is it the same pitot tubes used from the hydrant flow test? Are you flowing through 50-ft of hose to Hose Monsters? There will be some loss in that. Verify the gauge is working on the pump suction.
Consider removing the pump suction flange, and piping it out the door for a flow test to measure flow capacity. Calculate it like a stream straightener from 291, and use a C of 0.95. See how much flow you can actually get, and watch a static residual gauge on a nearby hydrant. If the results are normal then you should suspect that the issue is in the aboveground backflow and pump assembly. If the results are low, then the issue is likely in the new 8" underground lateral to the pump.

We have seen similar situations a few times. It usually ends up being an issue with the double check valve. Remove it temporarily and run the test. Keep eliminating variables until you are left with the culprit.

Reply
Michael Christensen
9/3/2026 01:48:34 am

I had a similar situation on a school that I did a couple years ago. We had the city check the PRV's that were installed. Initially they just checked the settings, eventually they checked the PRV and removed at least a fist-size of rust/gunk. This significantly increased the available fire flow.

Time of year is something to consider and ask about. I am aware of some water purveyors who adjust the PRV settings +5-psi seasonally in the summer time.

For better or worse to get to the bottom, it takes time and eliminating various things. There have been lots of good suggestions trying to isolate the item and suggest what is the issue. I recommend talking to the water purveyor because they commonly have modeled data which could be useful, just make sure that the data they give you is worth it (one time they said that 4,900 gpm can flow thru a 4-inch CI unlined that was over 80-years old)

I hope that helps in your quest to understand what is going on.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT