We have a number of apartment buildings, 4-5 stories in height, with fire pumps serving the standpipes coming towards their end-of-life.
Is there a code requirement to re-evaluate the water supply when replacing a pump in a like-for-like scenario? Of course, this building has no existing fire protection records or placards to reference. Thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Anthony
8/23/2024 07:14:50 am
First off you need to have placards in order to be able to know if your water supply is sufficient. That'll be an expensive hydraulic survey.
Reply
Glenn Berger
8/23/2024 08:11:08 am
The question "Is there a code requirement to re-evaluate the water supply when replacing a pump in a like-for-like scenario?" --
Reply
Jesse
8/23/2024 08:19:54 am
I'm not familiar with a code requirement to do so, but if I put my name on it you can bet I'm going to have an udated flow test.
Reply
Dan Wilder
8/23/2024 08:39:54 am
There is no word for word requirement for the entire pump (impellor, driver, controller) that I have seen, more inferred via sections like 25-23' below. At a liability standpoint, since this goes beyond component replacement, this would/should be a more detailed process.
Reply
Jimmy
8/23/2024 09:23:20 am
As an AHJ my suggestion;
Reply
Robert W Hughes
8/23/2024 01:00:23 pm
Hydrant Flow Tests cost $350 and up around here. FYI
Reply
Eric R
8/23/2024 09:43:14 am
You mention that the fire pump feeds standpipes. This leads me to assume the standpipes are automatic type, and if so, then they need to be flow-tested every 5 years per NFPA 25.
Reply
DLS
8/23/2024 10:51:22 am
I believe that in order to properly ensure the performance of the pump, an updated water supply evaluation should be provided.
Reply
Jack G
8/23/2024 12:18:12 pm
Of course you must meet or exceed the performance of the original test of the standpipe system.