Is a pull station required?
According to NFPA 72 (2019 Edition) § 23.8.5.1.2*, when connected to a supervising station, fire alarm systems employing automatic fire detectors or waterflow detection devices shall include a manual fire alarm box to initiate a signal to the supervising station. That said, for a non-sprinklered building, does the fire alarm control panel require a pull station near it/within the same room, or do adjacent exterior exit-door pull stations suffice? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Glenn Berger
10/1/2026 08:16:15 am
NFPA 72 Section 17.17.10.4 requires the pull station to be located within 5 feet of each exit doorway on each floor.
Reply
Todd Wyatt
10/1/2026 08:39:55 am
The requirements for MANUAL FIRE ALARM BOX(ES) are per the scoping Code (e.g. IBC-2024) per Chapter 9 Fire Protection and Life Safety Systems, Section 907 Fire Alarm and Detection Systems, 907.2 Where Required—New Buildings and Structures.
Reply
Todd Wyatt
10/1/2026 08:40:19 am
REFERENCES
Reply
Brett
10/1/2026 10:05:59 am
The pull station required in a fully sprinklered or smoke detected building (not requiring P/Ss throughout) is meant to facilitate alarm testing. In a building which requires P/Ss throughout, the intent is to use one of them for testing purposes. None would be required at the FACP unless it is mounted adjacent to an exit door which would normally require a P/S.
Reply
Jack G
10/1/2026 10:11:14 am
Per section 23.8.5.1.2 has the requirements for a single pull station.