Have 5 stories of parking with about 15 levels of residential floors above. For an enclosed, heated/conditioned garage we can use a wet system.
If we're using Extra Hazard Group 2 with high temp sprinklers or 11.2k sprinklers, which reduces our design area we know we need to account for "0.40 gpm/sqft x 2,000 sq.ft. = 800 gpm demand" at least. A PRV floor control valve like a 2-1/2" Zurn ZW5004 tops out at 500 gpm per the data sheet. Would it be possible to utilize two of these floor controls from different stairs and have an interconnected system on those levels? Or would it be better to utilize to try and separate the garage level sprinkler system from the standpipe for those levels and use a master pressure reducing valve station on ground level to feed the 5 garage levels? Would a redundant pressure reducing valve at a master pressure reducing valve station be necessary if the sprinkler feed is separated from the standpipe feed for those levels? Or could I just use a grooved 6" pilot-operated PRV like a Cla-Val 90G-21 (listed for 1763 gpm) before a floor control on garage levels? (a combined sprinkler/standpipe configuration) Lots to this, appreciate the feedback in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Jack G
10/6/2025 09:02:40 am
Yes a small redundant prv is required in parallel to a main prv.
Reply
Todd E Wyatt
10/6/2025 11:07:57 am
I recommend you first verify (from the Design Professional … Architect) the adopted scoping Code (IBC-2024?) to determine the requirements for the automatic sprinkler system (ASPS) as well as the standpipes systems (SS).
Reply
Todd E Wyatt
10/6/2025 11:08:37 am
REFERENCES
Reply
Brett
10/6/2025 12:55:28 pm
In order of the statements and questions:
Reply
Mark
10/6/2025 03:05:16 pm
Agreed
Reply
L Scott
10/8/2025 11:34:34 am
Responding to mostly Brett's thoughts here:
Reply