When Inspectors have an existing sprinkler system without a means to conduct forward flow, what is your process for addressing the test?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
6/2/2026 06:12:27 am
How is there no means?
Reply
Dan Wilder
6/2/2026 07:54:55 am
Inspection Report X
Reply
Anthony
6/2/2026 08:18:30 am
Assuming this is a backflow forward flow test? Then if the system was installed prior to the requirement ~ 15 years ago these means do not exist, just do a min drain test. The forward flow test is of dubious necessity to me.
Reply
Randy Kimbro
6/3/2026 10:08:43 am
Anthony, as an AHJ, I would respectfully disagree with the "dubious necessity". That annual requirement for a forward flow test provides assurance that the water supply can still meet the system demand of the sprinkler system. More than once we have observed a forward flow test that measured inadequate water supply and found either an underground obstruction or a closed valve at the street. We find this annual test very important.
Reply
Jack G
6/2/2026 08:35:32 am
Normally I turn the check valve
Reply
Jack G
6/2/2026 08:53:54 am
Generally try to sell them on a bypass around the check with a normally closed butterfly valve. If the fdc check is in a space that you could work on it.
Reply
Richard C. Iverson
6/2/2026 08:36:57 am
NFPA-25 (2017) Section 13.7.2.3:
Reply
Matthew Mueller
6/2/2026 08:43:47 am
NFPA 25 13.7.2.3 allows for "the maximum flow rate possible" when there are no connections available to accurately measure the flow rate. This can be as accomplished by opening up multiple main drains/ITV's. Obviously, this isn't the best solution, however it's allowable under the standard.
Reply