|
We have two fire pumps on a project which are to be connected to one emergency generator. One is a primary pump, the other is a backup.
Will these ever run simultaneously? The Electrical Engineer on the project is concerned about running supply for both pumps simultaneously and overburdening the generator. Is there an NFPA limitation for this, or requirement either way? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Glenn Berger
9/9/2022 08:12:33 am
Fire Pumps typically start on pressure drop, with the secondary pump starting on a further pressure drop and after the sequential start timer elapsed.
Reply
Jesse
9/9/2022 08:20:13 am
Its not ideal but it could happen.
Reply
Sanjeev
9/9/2022 08:59:08 am
Normally primary fire pump will be feed with normal power and backup fire pump will have own diesel engine or feed from emergency generator thinking both pumps can start together based on pressure drop settings.
Reply
Tim
9/9/2022 09:01:38 am
Yes, fire pumps can both run at same time if the the pressure in system drops below pre-set set start pressure of both primary and secondary pump set. The demand on electrical power is therefore doubled up.
Reply
In my experience duplicate pumps need 2 sources of power supply with demonstrable diversity in the supply arrangements and where supplies to each pump are controlled by individual automatic power transfer switches.
Reply
Franck
9/9/2022 09:14:56 am
Normally it shouldn't (otherwise the second would not be a back up, but a complement), but in reality it could happen, as indicated above.
Reply
DS
9/9/2022 09:33:34 am
The generator and overcurrent protection devices must be properly sized to handle the intended load. This includes both load from the primary and secondary fire pumps.
Reply
Greg
9/9/2022 11:09:03 am
Your one line diagram will be the best reference as design progresses. The electrical component selected for the automatic transfer switch will dictate how the pumps are called following power loss and emergency generator start.
Reply
Jose Manuel Cruz
9/9/2022 02:14:14 pm
The controller for each unit of multiple pump units
Reply
Rob B
9/12/2022 07:32:22 am
This squarely an issue for the EE to figure out. There is a fair amount of work that goes into generator load calculations and since it is a motor load, you have start up considerations and such.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
August 2026
PE PREP SERIES |
RSS Feed
