MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Video Scope Inside Dry Valve Satisfy Inspection?

6/8/2026

2 Comments

 
Doing inspections, does looking at the dry valve inside with a camera through, say, a drain (instead of removing the faceplate) and taking pictures satisfy the requirement for the inspections?

Most dry valves
nowadays have automatic resets, and the gaskets on the new faceplates are very, very thin and will not reseal even with the replacement part. FDC inspections also include check valves.

I don’t know why, but when you take the Vic off the check (FDC side), the groove coupling will not seal. So a lot of filing or replacement of the piece must be done. I'm thinking the pipe used was for threading and welding (not recommended for grooving).

Any insight here is appreciated, thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Thank You to Our Standout May Contributors

6/5/2026

 
A quick thank-you to this month’s top contributors for sharing their expertise and keeping the conversation moving!
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture

Code for ESFR Not Protecting Ignitable Liquids?

6/5/2026

7 Comments

 
Where in NFPA 13 or 30 does it say ESFR systems cannot protect ignitible liquids?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Is Dry Delivery Manifold Method Just Options?

6/4/2026

2 Comments

 
Under NFPA 13, 2019 Edition, does Section 8.2.3.1 provide the option of using 8.2.3.2, 8.2.3.3, 8.2.3.4, 8.2.3.5 or 8.2.3.7 to size the system?

Could I size an
800-gallon EH1 dry system to deliver water to a single test connection in 60 seconds based on 8.2.3.2, or must the system be calculated for water delivery by a recognized program per 8.2.3.5 and provide a 4-outlet test manifold with a 45-second time limit?

Is the manifold just an option? I've been confused on this for awhile...thanks in advance!!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

A Health Hazard for Systems without Backflows?

6/3/2026

7 Comments

 
Are there incidents of actual water health hazards from fire sprinkler systems?

I try to avoid waste. Backflow prevention devices are costly and also make sprinkler systems more expensive by adding friction loss, which can mean larger pipes. The water in most sprinkler systems is the same water as in the domestic system. Yes, the water in a steel pipe sprinkler system will get brown over time, because it picks up iron. Not pretty, but is that iron a health hazard? People buy Iron supplements.

In California the laws are confusing. Health and Safety Code - HSC § 13114.7 states: (b) Automatic fire sprinkler systems described in subdivision (a) shall not require any backflow protection equipment at the service connection other than required by standards for those systems contained in the publication of the National Fire Protection Association entitled “Installation of Sprinkler Systems” (N.F.P.A. Pamphlet No. 13, 1980 edition). and (a) states: (a) For the purposes of this section, the following are definitions of class I and class II systems:

(1) American Water Works Association (A.W.W.A.) Manual No. M-14 class 1—Automatic fire sprinkler systems with direct connection from public water mains only; no pumps, tanks, or reservoirs; no physical connection from other water supplies; no antifreeze or additives of any kind; and all sprinkler drains discharging to the atmosphere or other safe outlets.

(2) American Water Works Association (A.W.W.A.) Manual No. M-14 class 2—Automatic fire sprinkler systems which are the same as class 1, except that booster pumps may be installed in the connections from the street mains.

This makes sense, but unfortunately another section states: 13114.5 The governing body of any city or county may enact ordinances or laws imposing restrictions greater than those imposed by Sections 13113 and 13114. (Added by Stats. 1955, Ch. 1480.) AND many water purveyors, who are not city or county officials simply ignore the law. If you want to use their water, you abide by their demands! No single user wants to take the effort to fight. This can be really expensive, especially when a backflow is imposed on an existing system. The added friction loss can mean the whole system has to be recalculated, and often piping upgraded.

I would like to see the industry help to pass laws to eliminate backflows if they are not accomplishing anything.

Please share any ideas of who and how to help, or any examples if there are actual health issues. Thanks.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Procedure When No Means of Forward Flow Test?

6/2/2026

9 Comments

 
When Inspectors have an existing sprinkler system without a means to conduct forward flow, what is your process for addressing the test?
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

System-Side Hose Connection for Foam System?

6/1/2026

6 Comments

 
Is it acceptable to have a 2-1/2-inch hose connection on the system side of a low expansion foam system?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

FDC Check Valve Above-Ceiling Ever Allowed?

5/29/2026

4 Comments

 
In 1999, was it permissible to install a check valve above a ceiling with no access?

For context, our condominiums were built in 1999. The main sprinkler system has an FDC connection in front of the buildings. There is a check valve installed above the ceiling in the first condos in each building, with no access. 

​Was that ever permitted?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Do Gas-Burning Boilers Require Gas Detection?

5/28/2026

3 Comments

 
Do gas-burning boilers require gas detection above them?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

How to Connect Two Fire Pumps in Parallel?

5/27/2026

4 Comments

 
I have two sets of fire pumps (electric - diesel), one with a discharge of 1000 gpm and a pressure of 160 psi (11 bar), and the other with a discharge of 750 gpm and a pressure of 115 psi (8 bar).

How are these supposed to be arranged if they're to be connected in parallel?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Need PRV for Home Fire Sprinklers Over 175 psi?

5/26/2026

6 Comments

 
Greetings. My house was built in 2014 and has a fire sprinkler system with heads rated at 175, orange CPVC pipe throughout the attic, and a riser in the garage.

When I bought the home, pressures on the gauge were typically in the 155 psi range. Recently, they have been spiking to 185 and above. My fire line and domestic line separate early, right after the city meter at the street.

I installed a pressure relief valve, 175 psi, on the drain off the riser, and it has been dripping pretty constantly, about 1 drip every 10-20 seconds or so, depending on fluctuations in air temp.

When the pressure spikes, it brings it down to 175 pretty quickly. My question
 is, would you recommend I have a fire professional come out and install a pressure-reducing valve?

​Is that something that would be installed prior to the riser? Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Sprinkler Location with Wood Slatted Baffles?

5/25/2026

5 Comments

 
Hi all, I am looking for the right method to deal with a decorative wood slatted (open baffle) ceiling similar to the attached images. The slats are relatively deep and closely spaced, installed below the structural ceiling. I’m trying to determine the correct sprinkler approach in accordance with NFPA 13.

What's the best approach (or approaches) to locate sprinklers with baffles like this?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
5 Comments

Calc How Many Sprinklers for 13D Dry System?

5/22/2026

7 Comments

 
NFPA 13D calls for a minimum of 2 sprinklers to be hydraulic calculated.

​It does not appear that NFPA 13D requires extra sprinklers to be calculated for a dry pipe system.

Is this correct?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

ESFR Sprinklers Allowed for 63-ft Ceiling, in OH2?

5/21/2026

5 Comments

 
Can ESFR sprinklers be used in a manufacturing building that is 63'-0" high to protect an Ordinary Group 2 occupancy?

NFPA 13 2022 14.2.7 allows the use of ESFR to cover OH2 and lower occupancies, but I believe that those occupancies are located in storage areas or are incidental to the storage being protected. FMDS 3-26 and 8-9 allow their use up to 100 ft, but they do not classify ESFR sprinklers the same as NFPA.

​Any thoughts?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Calcs Required to Replace K3.9 with K4.2?

5/20/2026

10 Comments

 
I have a campus housing situation with a few thousand reliable 3.9k heads that are no longer made, on 16x16 spacing, requiring 17 gpm and 19 psi per the cut sheet.

We are looking to replace these with 4.2k sprinklers, same 16x16 spacing, is 16 gpm and 14.5 psi per the cut sheet.

Question is, I know the 4.2K falls just over the allowed 5% deviation, but these 4.2k sprinklers are more "efficient", so would they require running new hydraulic calcs to verify, or would it be safe to swap out as is?

​Thank you in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

High Static Pressure Without a Fire Pump?

5/19/2026

15 Comments

 
Has anyone encountered unusually high and consistent static pressures in sprinkler systems where there is no visible fire pump?

I recently came across two examples that raised questions:
- A riser in our major metro showing about 165 psi static pressure.
- A five-story hotel with roughly 125 psi static pressure on every level, consistently throughout the building.

In both cases, I searched extensively for a fire pump and could not find one. The buildings were on normal city water supplies, not private systems or campuses, and there was nothing obviously unusual about the sites.

It made me wonder whether there are situations where some type of booster pump is being used for sprinkler systems without being readily identified as a traditional NFPA 20 fire pump? Or perhaps there is another explanation entirely.

Has anyone else seen this? If so:
- What was the situation?
- Was there hidden pressure-boosting equipment involved?
- Are there municipalities or systems where this is more common?
- Or is there another explanation for maintaining these pressures throughout a building without a fire pump?

Interested to hear what others have encountered.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments

Allowed to Use Voice FA for Elementary PA?

5/18/2026

11 Comments

 
We've been called back for service work to a recent voice fire alarm system installation, where we found that the elementary school is using the voice fire alarm system as their public address system (announcements, etc).

Is there anything codewise that prohibits this?

On one hand, it should allow the system to possibly become more reliable since they'll report outages right away; I'm mostly just concerned with less trained staff using fire alarm equipment and having messages come from speakers labeled as "FIRE ALARM."

What are your thoughts on this?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Are “POTS in a Box” Systems Code-Compliant?

5/15/2026

7 Comments

 
With POTS lines going away very soon, I'm seeing many companies switch to a "POTS in a Box."

Do these meet the NFPA 72 code requirements?

I can't find much information about these devices. One thing I am finding is that they do not appear to be UL-listed.

At what point does NFPA 72 stop regulating the communication method?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Is Water Storage Tank Far from Pump a Problem?

5/14/2026

9 Comments

 
Hi, have you encountered cases where the fire pump is more than 100 ft (30 m) away from the water storage tank (underground)?

I know this isn't ideal. What type of pump or setup do you suggest or recommend in this situation?

​Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Minimum Height of Pipe in Underground Garage?

5/13/2026

9 Comments

 
Is there a minimum height requirement of pipes in an underground parking garage?

​Is that different than an ordinary occupiable space?

My vehicle is 75.8 inches tall, for instance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Route Diesel Fire Pump Flow Back Into Suction?

5/12/2026

5 Comments

 
I have a DoW project with specifications that require the diesel fire pump flow meter to discharge both into the pump suction and through the test header.

I don't have experience with this setup; in all my previous projects, the diesel fire pump discharged back to the water tank as well as to the test header.

I understand that NFPA 20 allows this arrangement (see attached figure from the 2025 edition), but I'm curious how it works in practice for two main reasons:

1. If we close the tank valve during testing, the pump's suction pipe will receive considerable pressure. Will this repeated pressure adjustment after each test impact the longevity of the soft packing, particularly regarding increased water leakage?

​2. How does a diesel fire pump cool its motor if the heat exchanger water isn't returned to the tank with fresh cool water coming in?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
5 Comments

Sprinkler Entire Attic With One Fuel-Fired Unit?

5/11/2026

9 Comments

 
Do you have to protect the whole attic that has smoke partitions with fire sprinklers if only one area has gas-fueled equipment in it?

​Can you just protect the one area that has the fuel-fired equipment in it?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
9 Comments

UFC 3-601-02/NFPA 2001 Clean Agent Inspection?

5/8/2026

2 Comments

 
Clean agent system inspections for Department of Defense (DoD) buildings require UFC 3-601-02.

Should NFPA 2001 inspection requirements also be included?

Looks as if the UFC 3-601-02 guidelines are more stringent than NFPA 2001, correct?

Trying to sort this out, thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Drop-Down Sprinkler for Coffered Ceiling?

5/7/2026

5 Comments

 
We have a coffered ceiling with a 3" drop as per design, and we'd like to have the fire sprinkler drop down 3" automatically when activated.

Is there a product or technique that can be used for this?

It's a high-end commercial space. Thanks in advance.

Moderator's Note: Updated "Chauffeured" to "Coffered." 


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Water Supply Options for Rural Area with Pond?

5/6/2026

13 Comments

 
I am working on a new building in a rural area that will require sprinkler protection. There is no access to a public water supply, only a 30-100 gpm well on site.

Options for fire suppression water include pumping from a large farm pond 150 feet away or installing
a 15,000-gallon water storage tank with a pump.

Any thoughts on
which option is more feasible and cost-effective​, or any alternatives we're not considering?

This is in a freezing climate. Thank you in advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
<<Previous
Forward>>
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT