Pipe Stands and Bracing I have a 12" fire pump that feeds the "U Turn" in the attached picture. Insurance company is adamant more bracing is needed.
My question is what size pipe stands are required for 12", and do I need more lateral bracing for the surge if the fire pump runs? All I can find in NFPA 13 only addresses up to 10". Any thoughts or ideas on codes I may be missing would be appreciated. Thank you! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
4/21/2025 08:31:20 am
As it falls outside of NFPA 13 scope, you'll likely need to go with an engineered stand approved for the pipe size and pipe weight. This may include needing a PE depending on your AHJ.
Reply
David Kendrick
4/21/2025 08:36:37 am
The challenge with an insurance reviewer making an engineering assessment of an installation.
Reply
Jesse
4/21/2025 08:38:32 am
Yeah, I agree with Dan. It seems like it falls outside the scope of 13. You'll need to have something engineered.
Reply
JackvG
4/21/2025 09:23:13 am
For a 12 inch fire pump discharge, NFPA 13&20 does not specify a pipe stand size. Instead the focus is on proper support and placement of the piping to prevent damage or displacement due to vibrations expansion or other factors ( consider weight and thrust on elbow and tee).
Reply