Pipe Size for Sprinklers Above & Below Ductwork?

10/18/2024

7 Comments

 
Doing a mechanical machine room, and I need to add sprinkler coverage above and below ductwork.

I was told that if you have 2 sprinklers (one covering above the ductwork and one covering under the ductwork), you can run 1-in pipe to each.

So here is the example: I have 4 sprinklers coming off a branchline but 2 of those are under ductwork. The uprights that are above and below are covering the same area.

What pipe size do I need to use for this branch line?

What code justifies this one way or another?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Brett
10/18/2024 08:14:00 am

Overhead sprinklers and sprinklers under obstructions should be calculated independently. The reason for that is that both sets of sprinklers aren't expected to discharge at the same time. If the number of sprinklers under obstructions isn't substantial, like in the case you've presented, then the size of the piping under the ductwork should match the sizing of the overhead system.

So, whatever pipe size has been calculated to supply two sprinklers on the overhead system should be used to supply two sprinklers below obstructions. If you have one pipe supplying four sprinklers and two are overhead with two below obstructions, it should be sized as if it were serving just the two overhead sprinklers.

1" may work for your project, but that shouldn't be used as a rule of thumb for every project. Sizing should always be based off hydraulic calculations unless you're altering a pipe schedule system. Even then, it would serve the public better to hydraulically calculate the system, but that's an entirely different topic.

Reply
Mike Morey
10/18/2024 08:16:09 am

Arguably you have to calculate one or the other (worst case) of the sprinklers above or below the obstruction. (see the first section below) Often the lower elevation will cancel out the added loss in the drop pipe, but you should at least contemplate that before deciding how to proceed. IE if you're flowing 20 gpm per head, what's the loss per foot in the pipe vs what's the gain in elevation. We often rule of thumb this stuff, but prescriptively you need to prove it, unless you go with (from NFPA 13 2022):
28.2.4.7.3.1
Sprinklers under the obstruction shall not be required to be included in the hydraulic calculation of the ceiling sprinklers.

28.2.4.7.3.2
Where the piping to sprinklers under obstructions follows the same sizing pattern as the branch lines, no additional hydraulic calculations shall be required for sprinklers under obstructions.

We often utilize the second item for storage etc systems, especially when we're not in the remote area so we don't have to do tons of calculations. If we have a line of sprinklers under an obstruction we drop once and run along it with pipe matching the overhead sizing.

Reply
Glenn Berger
10/18/2024 08:18:26 am

The easy answer to your question is 1 inch pipe to the 2 sprinklers below the ductwork would not raise too many eyebrows.

Reply
NK
10/18/2024 08:41:44 am

NFPA 13, 2025 added guidance to specifically address this situation for the first time:

§28.2.4.7.4.1 Supplemental sprinklers under the obstruction shall not be required to be included in the hydraulic calculation of the ceiling sprinklers.

§28.2.4.7.4.2 Where the piping to sprinklers under obstructions follows the same sizing pattern as the branch lines, no additional hydraulic calculations shall be required for sprinklers under obstructions.

§28.2.4.7.4.3 Where the requirements of 28.2.4.7.4.2 are not met, a level of supplemental sprinklers shall be calculated to verify pipe sizes.

(A) * The number of supplemental sprinklers shall include up to a maximum of four adjacent sprinklers attached to a branch line.

(B) For density/area applications, the area of coverage of each sprinkler shall only include the footprint of the obstruction it is protecting.

(C) For density/area applications, the design criteria shall be in accordance with Section 19.5.

(D) For CMSA and ESFR sprinklers, the discharge pressure shall be in accordance with 20.16.4.

(E) The level of supplemental sprinklers shall not be required to be balanced with the overhead system.

§19.5 Design Approaches for Supplemental Sprinklers.
When required to be included in the hydraulic calculations in accordance with 28.2.4.7.4.3, the design approach for supplemental sprinklers shall be permitted to be based on the hazard located directly below the obstruction.

Reply
Dan Wilder
10/18/2024 08:45:12 am

Depending on the applicable year of the adopted standard and what has been proven hydraulically.

It's a little grey for previous editions as to what you would calc the sprinklers beneath the obstruction to...If the overhead is calced a 130ft² (full floor coverage) but the sprinklers under the obstruction only need to provide coverage for 96 ft², does the lesser demand offset the loss through the extra pipe and fittings? Does calcing a line of sprinklers (individual feeds) beneath an obstruction (as that obstruction is a lesser sq ft in area) within the larger remote area mean the remote area needs to grow because you're not providing the correct density over the entire area as the uprights would or are up punished to provide the larger individual sprinkler coverage on sprinklers that do are covering lesser areas? How about ESFR sprinklers beneath duct as I often see a smaller pipe size to those sprinklers vs the overhead branch lines? Lots of examples to argue...

Run the calc for the branch line with the uprights and size accordingly, ignoring the sprinklers beneath the obstruction then apply the below sections.

If the hydraulic calcs show you can feed 1 sprinkler from 1", then then each pipe to a single sprinkler under the obstruction can be 1" as you do not need to calculate sprinklers under the obstruction per the below 13-2019 & 2022 (Chapter 28)
27.2.4.7.3
27.2.4.7.3.1
27.2.4.7.3.2 - Piping to sprinklers under obstructions specific.

If the hydraulics have say 1¼" sprigs to each sprinkler on the line or, unfortunately, when we run a grooved line with the same pipe size to the end, then (technically without any further calc support) the pipe sizing to any drops would also need to follow the same sizing of 1¼" UNLESS you can prove hydraulically a smaller pipe size (strictly following the standard).

The 13-2025 edition changes the requirements as these are now referred to as "Supplemental Sprinklers" in 13-2025 28.2.4.7.4 and now provides a means to run a calc to prove a smaller pipe size to sprinklers beneath obstructions via an "up to 4 sprinkler calc along a branch line" per 28.2.4.7.4.3.

And yes, in the past for a majority of my non-storge designs I have just run 1" to under obstruction sprinklers without any further proof.

Reply
Anthony
10/18/2024 09:03:24 am

New York is setback quite a bit with the NFPA year that is followed.

Some Jobs are 2007,2013 or 2016.

Typically, I had to use better judgement when sizing Branchlines.

The Layout of the heads underneath play a critical part in the sizing as well.

Lets say I have 2 Heads above and 3 Heads below of the same branch. Regular F1FR56 Uprights, 2 of the Heads that are underneath aren't close to the heads above.

I would Size the Branchline 1-1/2" to the 1st 3 Heads and then reduce down to 1" where applicable. Not sure if Pipe Scheduling would be easier than running a Hydraulic Calc to see if it ok with all 1inch.

A sprinkler fitter questioned me on it and honestly never really got called out on it.

Reply
Jack G
10/18/2024 09:49:50 am

Include only the highest demand from either the above or below sprinklers per NFPA 13. If 1 inch branch, then the additional line pipe can be 1 inch.
For standard or qr sprinklers.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT