I'm working on a tenant improvement for a retail storage for a very large & common phone company. The architectural plans list the occupancy as Business.
I’ve designed one of these before, and when I pulled up the drawings from that previous job, the architect labeled it as Mercantile, so I designed it at 130 sqft spacing under Ordinary Hazard Group 1. Now, on this current project, there's no mention of Mercantile—only Business. The space is straightforward: a sales floor and a restroom in a 1,218-square-foot area. Can this be designed as Light Hazard? Looking at NFPA 13 (2019), Section 4.3.3 – Ordinary Hazard (Group 1) (using NFPA Link), the enhanced commentary refers to OH1 as covering “most light manufacturing and service industries where the use of flammable and combustible liquids or gases is either nonexistent or very limited.” That doesn’t really sound like a retail cellphone store to me. Even in the Annex, A.4.3.3 OH1 (6): Electronic Plant—this doesn’t seem anywhere near that level of hazard. Could someone help me out here? I get that I could just design to 130 sqft spacing and be safe, but I’m really aiming to understand and apply the right classification—not just overdesign. Trying to be the best, most informed designer I can be. Thanks for your time and any insight! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Chad
8/1/2025 08:02:50 am
Are they usually selling things that you can take away? Is merchandise on display? If yes then its mercantile.
Reply
Wes
8/1/2025 08:10:35 am
A caution here - Building Occupancy, as defined in the IBC, is relevant architecturally. It's designated by the architect (or a code consultant) for purposes of classifying risk for a building.
Reply
jakob cirell
8/1/2025 08:20:31 am
Occupancy Classification through NFPA 13 seems like the proper route. I would also look into whether you need to go the route of commodity classification, if there is storage of significant amount of electronics with lithium-ion batteries.
Reply
Chad
8/1/2025 08:27:47 am
Its OH2 all day in my opinion because mercantile is listed as you said in the annex and that is how I enforce it locally.
Reply
Glenn Berger
8/1/2025 08:35:00 am
You got some pretty good responses from Chad & Wes already. Building / Room names are good to have, but the actually way the space is being utilized must govern.
Reply
Dan Wilder
8/1/2025 08:39:47 am
Without knowing the building construction, this is a guess.
Reply
Joe
8/1/2025 10:19:16 am
Too often people interpret a fire sprinkler class with what is happening in a space or the likelihood of fire. In actuality sprinkler hazard classification is dependent upon heat release. The appendix of NFPA13 gives unofficial rule of thumb guidance. However since heat release is rather significant calculation, this is the reason that this portion of "design" is often considered "Engineering". This decision can be made with full blown specific calculations or an educated opinion. For this reason I eventually grew fond of collaborating with an engineer to make my design decisions with full confidence. This doesn't answer your question does it?
Reply
Joe
8/1/2025 10:24:08 am
BTW - The building code is a system, so you also have to confirm what requirements the overall building design requires or has taken advantage of tradeoffs.
Reply
Chad
8/1/2025 10:39:50 am
that's fair... Would you agree that even a sparsely filled sales floor (like this) will be adequately protected by 0.1GPM/SQ FT but the stock rooms will need 0.2PGM/SQFT because that is really the bulk source of heat release potential.
Reply
Peter Howard
8/1/2025 10:21:47 am
I'd default to ordinary if it's retail space. But Dan Wilder has given the "correct answer" here. The architect's code analysis sheet should be the dominant guideline.
Reply
Jesse
8/1/2025 10:30:14 am
The B occupancy is from IBC. In Automatic Sprinkler design, we typically don't design to IBC as that's used primarily to identify WHEN sprinkler protection is required. The HOW to protect it is from NFPA 13.
Reply
Gary Sims
8/1/2025 10:30:22 am
What Wes and Chad said above. Wes nailed it... but as Chad stated, be an owner advocate and set them up for success in the future. Dan is also correct. I love this platform!
Reply
Jon N
8/1/2025 01:49:25 pm
Some great comments have been made here and this is an area that I have some interest in. Building/fire code occupancy classifications, NFPA 13 commodity hazards, and the reality of fuel loads do not always correlate. For instance, review the NIST studies and videos on office cubicle fires. The heat release rates (HRR) on these fires often exceeded 6MW yet NFPA 13 protects office uses with light hazard density. One of the original tests on retail / mercantile fires was from Europe (England?) where a rack of clothing was burned with a HRR of around 5MW (sorry, I don't have the exact report in front of me). That became the basis for mercantile needing to have greater protection criteria. So, my question becomes, if light hazard fire sprinkler density can protect office fires with a higher HRR, why can't they protect a low-risk cell phone store. All too often we get hung up on definitions and the technical requirements of the codes and standards and we ignore "common sense" and fire physics. To quote one of the nation's greatest fire protection engineers (Bud Nelson - RIP): "If the answer defies the laws of fire physics or common sense, the answer is wrong."
Reply
Dan Wilder
8/1/2025 03:12:04 pm
Wait....so all my fire protection paperwork in my office (vertical/horizontal loose and tight rolled paper storage, shelving, the open file cabinet under my desk that magically gets filed over every weekend...) isn't protected FROM fire?!?
Reply
Jeff Ayers
8/1/2025 02:34:37 pm
Did the EOR specify the classification? Even in a delegated design, the EOR specifies the classification of light, ordinary hazard etc. on which you base your sprinkler bid.
Reply
Jack G
8/1/2025 06:07:46 pm
It’s all been covered above.