MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Phantom Flow for QR Reduction & Attic Systems?

2/24/2025

9 Comments

 
Is the additional flow described by NFPA 13 27.2.4.2.5 (2019) based on the original minimum design area or the minimum area after modifications?

Say I have a light hazard system with low ceilings. The default minimum area is 1,500 sqft but is reduced to 900 per Section 19.3.3.2.3.1. The calculation on the sprinklers in that 900 sqft area results in 128 gpm total flow (not including the hose allowance).

If the additional flow in 27.2.4.2.5 is based on the original 1,500 sqft
, then I would need to add 22 gpm of extra flow on the main to get the minimum of 150 gpm running through the main.

If the additional flow is based
on the 900, then I'm already meeting the requirement of 90 gpm, and I can ignore the additional flow requirement.

Similarly
, we start at 1500 sqft in a dry attic system, but it needs to be increased to 2,535 sqft minimum due to the dry system and sloped ceiling.

Will the minimum flow as per 27.2.4.2.5 be 150 gpm or 254 gpm?

This sometimes comes up when using specialty attic sprinklers, which allow for fewer operating sprinklers in the calculation. It comes down to the definition of "minimum design area".

Is this the original minimum area, or the modified minimum area?

In my designs I've been defaulting to the larger of the two demands to be conservative, but what is the actual intent of this clause?

I haven't found any discussions relating to the changing of the minimum design area.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Zachary Bishop
2/24/2025 08:30:59 am

The way this reads to me is the minimum design area as modified. Since, the "minimum" design area required is allowed to be increased / reduced in the situations you mention, it makes sense that the phantom flow requirement would change as well to match the requirements for the current situation.

Reply
Pete H
2/24/2025 09:06:02 am

I'd agree with Zachary and go with design area as modified.

Especially in the case of the dry system.

Reply
Dan Wilder
2/24/2025 09:12:03 am

It is based on the "Minimum Design Area", so the final area after adjustments. I had to look back to the Ken Isman article that does reference an area reduction (high temp sprinklers for an Extra Hazard classification) which leads me to think it's the final minimum design area, not the starting point.

"Minimum Area" is only referenced in 19.3.3.1.5.1 / 19.3.3.1.5.2 in relation to the 3000ft² area for unsprinklered concealed spaces. "Minimum Design Area" is only referenced in 19.3.3.2.2.3 for EC sprinklers.

I would argue that a specialty design, like attic sprinklers, are not Density/Area based, more special application, and are not required to apply this section.

Reply
Jesse link
2/25/2025 08:08:17 am

Yeah I agree with Dan here, especially in the case os special application sprinklers. These are not Density / Area based

Reply
Casey Milhorn
2/24/2025 11:59:03 am

I agree with Dan and others. It's based on the final reduction or increase. As far as dealing with listed design approaches that are based on a listed system/product, then no, you would not add phantom flow. These listed design approaches have been tested and approved as listed.

Reply
Jack G
2/24/2025 03:30:52 pm

Here s the way i approach it.
I think its a rarity that i use it. Also where you add it depends on which version of 13 you use.
Common sense should also be used.
If you can use " large room rule", or "area reduction method/ qr heads" , phantom flow should not be added. These are acceptable calculation methods.
Where i find myself using it is say you are doing a modification of a small area within a larger area.
Like a strip store, or a light hazard area. So say there are partitions where you cant get in or trace piping. Like licked tenant areas. So say its a 650 ft2 modification. At .1 density the modifiedvarea needs 70 gpm (when i calculate this area only)
The 1500 ft2 normal area requires 150 gpm. ( .1×1500) So phantom flow to be added is 150-70 = 80 gpm.
So i add the 80gpm to my calculated area ( only in the renovated area ) and i add it to the appropriate point ( depending on 13 version) ,, be it branch line or where the main splits.
Saves on finding a lot of keys , retracing system, or entire system calculations.
I thought the 2013 version and appendix explaines it so " our heads dont hurt "! Opinion.

Reply
Jack G
2/24/2025 03:58:38 pm

Looking at you dry attic with sloped roof, this area and sloped ceiling increases is for the “ dry system” and the “ ceiling slope”.
Where it matters is say attic/ and light hazard system below.
If the attic system has a home run supply, say from the riser room
then phantom flow would not need to be added. ( full size main)
So where phantom flow would be used for is to compensate for situations where a smaller area with a higher density is being protected within a larger area, less demanding sprinkler system .
This is relevant in say attics with a smaller design , or attic sprinklers giving a smaller area based on a minimum number of sprinklers over a smaller area. ( adding flow / potential fire load ) even though a smaller amount of sprinklers may be activated .

Reply
Jose figueroa
2/24/2025 05:37:58 pm

I read the exact same question on reddit.com.

I have try to understand the concern of the NFPA13 (2019) clause. I quote “ 27.2.4.2.5
Where the total design discharge from these operating sprinklers is less than the minimum required discharge determined by multiplying the required design density times the required minimum design area, an additional flow shall be added at the point of connection of the branch line to the cross main furthest from the source to increase the overall demand, not including hose stream allowance, to the minimum required discharge”

I went straight to the NFPA to understand the intent of this clause. I believe this is thr core issue.

Putting it the simplest way,

Reply
Jose Figueroa
2/24/2025 07:11:11 pm

I'm sorry. I posted without finishing my post: If the total design discharge from the sprinklers is less than the minimum required discharge, this means there's insufficient water flow to properly suppress the fire. To compensate for this deficiency, additional water flow must be introduced.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT