Phantom Flow for a 750 sqft Paint Spray booth?

12/11/2024

6 Comments

 
Does Phantom Flow apply to a 750 sqft Paint Spray booth?

Currently acting as AHJ for a spray booth sprinkler submittal. We commented that their hydraulic calculations must comply with 2022 NFPA 13 Sections 28.2.4.2.4 and 28.2.4.2.5.

Are we correct in our interpretation that Section 28.2.4.2.5 requires an additional flow to be added, like a secondary hose stream allowance, so that the design discharge meets the minimum required discharge?

In this specific submittal, it would require an Extra Hazard Group 2 (EH2) spray booth (approximately 750 square feet in area) to add additional flow in the calculation to meet the minimum EH2 design discharge of 1,000 gpm? (ie: 0.40 x 2500 = 1,000 gpm).

The Appendix material seems to confirm this interpretation. It seems like overkill, but I cannot find an NFPA Section that would allow the minimum design area (2500 sqft) to be reduced for calculation purposes, even if the spray booth itself is only 750 sqft.

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Brett
12/11/2024 06:28:35 am

Phantom flow is specific to the density/area method. If the density/area method is being used then phantom flow is required. If the room design method is being used then phantom flow is not required.

Reply
Dan Wilder
12/11/2024 07:11:59 am

I would argue that if the booth falls under NFPA 33 (per 13-22 27.5), then the design provisions of the calculation area as defined within 33-19' 9.5.1 would not require it. If it referenced back to NFPA 13 for hydraulic calcs then I would apply it as you have stated.

33-19'-9.5.1.2 does define the booth spray areas as EH2

33-19'-9.5.1.2.1 states the design area shall not be required to exceed the area of the booth or room where the application is being conducted.

So if the calculation area is only the booth per 33, then the EH2 minimum design area within 13 does not apply, nor would the sections 28.2.4.2.4 & 28.2.4.2.5 for not meeting that minimum.

Reply
Jaymie
12/11/2024 08:29:38 am

I think you're talking about two different things. Your design area would be .40 for 750 square feet. Your hose stream allowance for extra hazard is 500 gpm for 90 minutes so water needed when combined is 72,000 gallons.

Reply
Jesse
12/11/2024 08:58:54 am

I don't think phantom flow applies here, or at least I would pursue avennues for it not to apply. Further, I don't think the spirit of phantom flow would be appalicable.

First, if room design method is being used, phantom flow wouldn't ever apply as phantom flow is specific to CMDA designs.

Secondly, I think 33 would be a more appllcable code which doesn't require phantom flow.

Reply
Anthony
12/12/2024 09:04:09 am

I agree with Jesse here. the phantom flow for a fixed known hazard like a spray booth would not require enlarging the main to carry the added capacity.

My guess is that this section of the standard is to allow for convenient future expansion of the high hazard area. For a fixed paint booth in a small shop, I'd ask for variance. Seems counter productive and costly. I would hope this item is removed or given an "if allowed by an ahj this item will not be required" in the future editions of 13

Reply
Jay
12/11/2024 09:24:08 am

I had this same situation last Fall in an electric vehicle collision repair/body shop facility. I sent the questions to the NFSA, about whether or not the EH2 spray booth design was required to extend 15ft outside the booth (adjacent hazards) and if a phantom flow was required to be added due to the spray booth size (about 400 sqft) the design flow was well under the minimum 1000gpm of an EH2.
Here is their response (design area extension not required and phantom flow not required):

The answer to your question is yes, only the sprinklers within the spray booth or room are required to be calculated.

As you mentioned section 9.5.1.2.1 states “ The sprinkler design area shall not be required to exceed the area of the booth or room in which spraying or resin application is conducted”.
Section 9.5.1.3 states that “the water supply shall be sufficient to supply all sprinklers likely to open in any one fire incident without depleting the available water for use in hose streams.”
The Annex material for section 9.5.1.3 further clarifies the intent by stating “Building areas outside of the spray area or paint booth are not included in the demand calculations, as the fire suppression systems and booth/spray area construction are intended to contain a fire until manual fire-fighting efforts can achieve final fire extinguishment.

While NFPA 13 does provide a larger area for these densities, the fact that NFPA 33 provides specific design area constraints takes precedence.

Section 5.2 of NFPA 33 requires spray rooms to have a 2 hour rating. Additionally Section 5.3.2 requires walls and ceilings of spray booths constructed of sheet metal to have no thinner than 1.2 mm or two layers no thinner than .09 mm.

So long as these areas meet the requirements for a spray booth or spray room, the calculations are not required to extend beyond that area.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT