MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Phantom Flow for 4-Sprinkler Fire Pump Room?

10/16/2024

10 Comments

 
I am working on a project with a diesel fire pump room that is Extra Hazard 2 (0.4 gpm / 2500 SF). The room is only 300 SF, which is well below 2,500 SF.

The 2022 Edition, NFPA 13 28.2.4.2.4, indicates following a set of steps shown in A.28.2.4.2.4. This section indicates that if the flow is less than the minimum required flow, then the difference in flow must be added to a node on the system. A.28.2.4.2.5 shows a picture example of where to add the flow.

The current design has 4 sprinklers within the room, each discharging around 30 gpm ((0.4 gpm x 300 SF) / 4). When reviewing the shop drawings, 880 gpm was added to a node, increasing the system pressure to about 150 psi!

How is NFPA 13 28.2.4.2.4 supposed to be accurately calculated within the hydraulic calcs?

Do you create an imaginary system and, in this case, add 21 more sprinklers for a total of 25 (2500 / 100 SF per sprinkler)?

Adding the 880 gpm to the system shown on the shop drawings and getting a required pressure of about 150 psi doesn't seem right.
Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Brett
10/16/2024 06:32:54 am

To answer your question, yes that is how it's supposed to be done as long as the flow is added at the appropriate point.

My question to you is why are you calculating just these four sprinklers? If you're calculating via the room design method then there is no need to account for phantom flow. If you're using the density/area method then the design area should be extended to the appropriate size.

Reply
Anthony
10/16/2024 07:59:29 am

See below for the relevant code (NFPA13-16). You are correctly calculating just the hazard area as you have partitions separating the hazards.The point of the 'ghost flow' is to ensure the 'main' is sized for the hazard.So in this case add it jsut bast you 2 branch lines. I'm not an expert in hydracad or sprinkcad, not sure which you're using but you could just add a fake sprinkler or several flowing hoses to size the main there.

You could also just do the math by hand. To size the main properly.
At 1000 gpm you lose:
.1965 PSI/ FT through 4'' sch 10
.028 PSI/FT through sch 10 6''
.0078664 PSI/FT through 8'' sch 10



23.4.4.2.4* Where the available floor area for a specific area/
density design criteria, including any extension of area as re-quired by 11.1.2 and Section 12.3, is less than the required minimum design area, the design area shall be permitted to only include those sprinklers within the available design area.

11.1.2 and 12.3 say you have to extend the design area if not separated. This case clearly has a separated hazard. It would be wrong to extend an extra hazard density outside the fire pump room in this case.

23.4.4.2.5 Where the total design discharge from these operating sprinklers is less than the minimum required discharge determined by multiplying the required design density times the required minimum design area, an additional flow shall be
added at the point of connection of the branch line to the
cross main furthest from the source to increase the overall
demand, not including hose stream allowance, to the minimum required discharge


I think you'd be fine asking the AHJ if you can size the main just for those sprinklers in that area as you are right at the pump not some remote warehouse location.

Reply
Dan Wilder
10/16/2024 08:11:29 am

Brett nailed it but some food for thought.

The procedure is mostly correct, the application is incorrect. In this case, the fire pump room should be rated (NFPA 20 - 4.14.1.1.2), thus allowing for room design method (19.2.3.3.3 & 19.2.3.3.5) and avoiding the "Phantom Flow" requirements.

If "Phantom Flow" was being applied, I would also be using any available reductions (high temp sprinklers per 19.2.3.2.6, 11.2K sprinklers or greater per 19.2.3.2.7 for extra hazard area reduction of 25% but no lower than 2,000FT²). Then, .4 x 2000 = 800GPM (total required per 28.2.4.2.5). The 4-sprinkler discharge of ~120GPM would mean that the additional required GPM is only 680 GPM (800GPM - 120 GPM).

Some previous discussion for Phantom Flow

https://www.meyerfire.com/daily/could-someone-please-explain-phantom-flow

Reply
Mike Morey
10/16/2024 09:24:34 am

As usual Dan beat me to it, but this is the way to go. Room design method is not Density Area and thus not subject to phantom flow.

Reply
RayJ link
10/16/2024 09:42:53 am

Dan seems to beat a lot of people around here!

Brett
10/16/2024 09:49:53 am

The only caveat with the room design method is that the rating of the room has to be equal to or greater than the required water supply duration. If the room is EH2 (90 minute water supply required assuming it's electronically supervised) and it has 1 hour rated walls, then the room design method cannot be used.

Reply
Mike K
10/16/2024 03:18:29 pm

The room is 2 hr rated. Thanks for the input!

Reply
Jessica Lutz
10/17/2024 11:42:06 am

Wilder on point again. ....came here to comment on the Pump room 2-hr rating requirement.

Reply
Jack G
10/16/2024 09:03:47 am

MeyerFire 5/7/2020 indicates the design density should be. .25 for a diesel fire pump. I would try submitting that wit “ room design method”.
A .40 would be per the spec——- but room design method.
I m not a believer in phantom flows.
A sprinkler system does not have a switch controlling the flow. If one sprinkler goes off, it’s getting many times the density.
Try doing a supply calc ( best description of system flow ) . Especially with a 10 psi safety factor)
You will find the supply calc exceeds the water supply and your NFPA 13 demand calc.
Pipe sizing can control water flow.
Same with phantom flow.

Reply
Jesse
10/16/2024 09:08:14 am

I love these threads that make you think. Topics like these are ones I kind of forget about until we need to do it.

Agree with Dan and his statement about the application being wrong.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT