A 4-inch schedule 40 main is routed parallel in-between two beams and requires a trapeze hanger. The main is 2 ft. from one beam and 8.5 ft from the other for a total span of 10.5 ft. What is the smallest schedule 10 pipe capable of supporting this main as a trapeze hanger? a. 2 inch b. 2-1/2 inch c. 3 inch d. 3-1/2 inch Solution | Posted 10/12/20
4 Comments
B
10/9/2020 08:04:43 am
A.
Reply
D
10/9/2020 10:23:39 am
B.
Reply
Travis
10/9/2020 11:00:31 am
A (per NFPA 13 Tables 9.1.1.7.1(a) and 9.1.1.7.1(b)). I'm pretty sure that all the details related to the beams is extra to throw you off. Certainly interested in hearing if you disagree with that.
Reply
Joe
10/12/2020 05:53:11 am
B
Reply
Leave a Reply. |
Free SignupSubscribe and learn something new each day:
CommunityThank You to Our Top
October '20 Contributors!
Your PostThe ToolkitSprinkler Designer or Engineer?
Get all of our tools, including the Sprinkler Database, Friction Loss Calculator, Fire Pump Analyzer and more: Filters
All
Archives
January 2021
Daily
Daily discussions are open-ended fire protection, fire alarm, and life safety questions submitted anonymously for the benefit of sharing expertise and learning from other perspectives. Anyone can submit a question here:
Exam Prep2020 PE Prep Guide
(Available Now!) PE Prep Series
(Available Now!) 2020 PE Prep Series
Current Leaderboard (Click to enlarge) PE Problems
Visit July-October for daily Fire Protection PE Exam sample questions.
Solutions are posted the day after posting. Comment with your solutions, questions or clarifications. Please note that questions posted are unofficial and in accordance with NCEES rules are intended to be similar to actual exam questions, not actual exam questions themselves. |