In which of the following scenarios is neither explosion protection nor suppression system required? a. Flammable paint warehouse mixing rooms where open transfer of paint occurs b. Dust ventilator equipment where the dust density can be above its lower flammability limit c. Mechanical room where service equipment is subject to explosion d. All of the above require either explosion protection or suppression systems Solution | Posted 10/05/20 d. All of the above require explosion protection or explosion suppression systems, as each scenario is considered equipment or an area where hazardous processes or storage can introduce explosion potential. NFPA 101-2018 Section 8.7.2 establishes the requirement.
6 Comments
B
10/2/2020 09:57:26 am
C.
Reply
NinaB
10/4/2020 07:11:47 pm
d.
Reply
B
10/5/2020 08:11:10 am
NFPA 101, Sec 12.3.2.1.1, specifically allows the use of fire barriers in lieu of sprinklers when protecting mechanical rooms that contain equipment subject to explosion.
Reply
S
10/5/2020 09:38:59 am
I agree! Although I believe this to be one of their popular "trick questions" on the NICET test; since it did not specify the wall type or thickness of the mechanical room. possibly?
Reply
D
10/5/2020 10:30:25 am
This is a requirement for New Assembly Occupancies and is not applicable here.
Reply
joe
10/5/2020 04:21:01 pm
d
Reply
Leave a Reply. |
Free SignupSubscribe and learn something new each day:
CommunityThank You to Our Top
February '21 Contributors!
Your PostThe ToolkitSprinkler Designer or Engineer?
Get all of our tools, including the Sprinkler Database, Friction Loss Calculator, Fire Pump Analyzer and more: Filters
All
Archives
April 2021
Daily
Daily discussions are open-ended fire protection, fire alarm, and life safety questions submitted anonymously for the benefit of sharing expertise and learning from other perspectives. Anyone can submit a question here:
Exam Prep2020 PE Prep Guide
(Available Now!) PE Prep Series
(Available Now!) 2020 PE Prep Series
Current Leaderboard (Click to enlarge) PE Problems
Visit July-October for daily Fire Protection PE Exam sample questions.
Solutions are posted the day after posting. Comment with your solutions, questions or clarifications. Please note that questions posted are unofficial and in accordance with NCEES rules are intended to be similar to actual exam questions, not actual exam questions themselves. |