Which of the following types of pipe would require the most hangers for the same length of 1-1/2" pipe? a. CPVC b. Copper Tube c. Steel other than Threaded Lightwall d. Threaded Lightwall Steel Solution | Posted 08/10/18
6 Comments
SD
8/9/2018 09:11:03 am
Answer: a
Reply
MIGUEL ARTURO NUNEZ
8/9/2018 09:49:03 am
Answer: a
Reply
Edw H
8/9/2018 09:58:42 am
NFPA 13-2016 9.2.2.1(a) CPVC 7'-0"
Reply
IW
8/9/2018 10:02:00 am
A
Reply
Pari
8/9/2018 11:15:21 am
A Table 9.2.2.1
Reply
Colleen
8/9/2018 11:16:51 am
Concur, A. CPVC.
Reply