An existing warehouse storing flammable and combustible liquids, considered high-hazard storage, has a ramp at the back of the building used for egress. If the ramp serves an egress load of 79 persons, what is the required minimum ramp width? a. 30 inches b. 31.6 inches c. 39.5 inches d. 40 inches Solution | Posted 09/14/20
8 Comments
KK
9/8/2020 08:56:45 am
B. 31.6 inches
Reply
Joe
9/8/2020 09:40:07 am
B
Reply
NinaB
9/8/2020 11:11:46 am
b.79x0.4=31.6"
Reply
RYAN
9/8/2020 03:29:47 pm
B
Reply
NearEngineer
9/8/2020 06:30:38 pm
B
Reply
SK
9/8/2020 07:52:36 pm
B
Reply
Naruto
9/9/2020 11:24:02 pm
b
Reply
Ver Fungo
9/16/2020 07:14:08 pm
As per Table 7.3.3.1 Capacity factors, High hazard the width per person is 0.4. x 79 person = 31.6 in.
Reply
Leave a Reply. |
Free SignupSubscribe and learn something new each day:
CommunityThank You to Our Top
October '20 Contributors!
Your PostThe ToolkitSprinkler Designer or Engineer?
Get all of our tools, including the Sprinkler Database, Friction Loss Calculator, Fire Pump Analyzer and more: Filters
All
Archives
January 2021
Daily
Daily discussions are open-ended fire protection, fire alarm, and life safety questions submitted anonymously for the benefit of sharing expertise and learning from other perspectives. Anyone can submit a question here:
Exam Prep2020 PE Prep Guide
(Available Now!) PE Prep Series
(Available Now!) 2020 PE Prep Series
Current Leaderboard (Click to enlarge) PE Problems
Visit July-October for daily Fire Protection PE Exam sample questions.
Solutions are posted the day after posting. Comment with your solutions, questions or clarifications. Please note that questions posted are unofficial and in accordance with NCEES rules are intended to be similar to actual exam questions, not actual exam questions themselves. |