What length of 6-inch Schedule 40 black steel pipe would provide the same friction loss as 24 feet of 4-inch schedule 10 black steel pipe if both are serving a wet sprinkler system at the same flow rate? a. 4 ft b. 34 ft c. 135 ft d. 173 ft Solution | Posted 08/28/20
4 Comments
J
8/27/2020 09:49:07 am
134.0826286
Reply
NinaB
8/27/2020 10:48:06 am
c. Pf.l.=134.62 ft=135 ft
Reply
SK
8/28/2020 11:36:11 am
C
Reply
JR
8/28/2020 03:42:47 pm
Why are they using the formula for Hazen-Williams Pressure Loss and not friction loss, like the question asks? If you us the friction lost equation (Darcy-Weisbach) you would get answer (b) 34 ft?
Reply
Leave a Reply. |
Free SignupSubscribe and learn something new each day:
CommunityThank You to Our Top
February '21 Contributors!
Your PostThe ToolkitSprinkler Designer or Engineer?
Get all of our tools, including the Sprinkler Database, Friction Loss Calculator, Fire Pump Analyzer and more: Filters
All
Archives
March 2021
Daily
Daily discussions are open-ended fire protection, fire alarm, and life safety questions submitted anonymously for the benefit of sharing expertise and learning from other perspectives. Anyone can submit a question here:
Exam Prep2020 PE Prep Guide
(Available Now!) PE Prep Series
(Available Now!) 2020 PE Prep Series
Current Leaderboard (Click to enlarge) PE Problems
Visit July-October for daily Fire Protection PE Exam sample questions.
Solutions are posted the day after posting. Comment with your solutions, questions or clarifications. Please note that questions posted are unofficial and in accordance with NCEES rules are intended to be similar to actual exam questions, not actual exam questions themselves. |