Under NFPA 13, 2022: in noncombustible stair shafts, can sprinklers be omitted at the entire bottom area of the stairs?
For example, if the first floor is the bottom of the stairs, can sprinklers be omitted under the second floor at the area where you enter the stairwell? Section 9.3.4.2.3.1 states, "Sprinklers shall be permitted to be omitted from the bottom of the stairwell when the space under the stairs at the bottom is blocked off so that no storage can occur." Is this only referring to under the intermediate landing and not the entire first floor area of the stairs? I know that at the beginning of this Section 9.3.4.2.1 states in part "under the first accessible landing above the bottom of the shaft." So does the omission apply in this case? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
4/27/2026 08:15:00 am
This clause can be used throughout the entire bottom of the stair enclosure as long as no space exists where storage can occur. (typically it is for "open space" below treads or landings above.
Reply
Dan Wilder
4/27/2026 08:15:41 am
Without the help of a visual, I'll do my best to describe....I have seen several variations of what was sprinklered.
Reply
anthony
4/27/2026 09:35:17 am
I agree with Dan here. specifically the following:
Reply
Blaine
4/27/2026 09:45:49 am
I’m running up against this as a reviewer. The problem I have is exactly what Dan describes- How do you regulate blocked. Our fire dept inspectors don’t think I a rail is sufficient to prevent storage. I agree and have stated that I was looking for something more substantial that actually prevents someone from stashing the snow blower or Christmas decorations under the stairs.
Reply
Mark Harris
4/27/2026 09:54:02 am
Well said on the cleaning carts Anthony. Lol. Blaine my background is the contractor side but if I was an AHJ to me to avoid a sprinkler you would need to block the under stair landing from any storage with a stud wall. Something permanent.
Reply
Chris Dorsey
4/27/2026 10:43:13 am
I tend to agree about the need for a sprinkler under the main landing for the floor above. What is causing me to question this is the commentary added to the Handbook (only version I have is 2016, and I realize the commentary is not considered part of the standard).
Reply
Jack G
5/1/2026 07:12:56 am
Whether combustible or not FM global recommends a sprinkler at the floor landing.