If a bathroom is greater than 55 sq ft, but is compartmentalized into spaces less than 55 sq ft each, does the exemption from coverage apply to the compartments (assuming all other requirements apply)?
We have a bathroom where the toilet is separated from rest of the bathroom. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
12/3/2024 07:32:59 am
Would need to know which NFPA and IBC/NFPA building code is being applied, including year, as they do differ a bit in application and omission allowances. Also need to know what the building occupancy is to answer.
Reply
Pete H
12/3/2024 08:15:02 am
To echo what Dan's saying: yes, as long as the omission for one of them is valid and the compartmentalization meets the standards of the codes and standards.
Reply
Jesse
12/3/2024 08:44:27 am
Would need rto know the occupoancy and relevant code section applicable to the project
Reply
Glenn Berger
12/3/2024 08:48:45 am
Like other have already said, need more information on the project and applicable codes. But in this case, the potential allowance for the elimination of a sprinkler or a few sprinklers is not worth it.
Reply
Anthony L. Crispo
12/3/2024 09:36:00 am
I have this situation in a 20+ story hotel would eliminate 360~400 sprinklers depending on final layout. IBC 2018 and NFPA 13-13.
Reply
Dan Wilder
12/3/2024 10:29:20 am
Then omission is allowed per IBC 2018-903.3.1.1.2 when designing to NFPA 13
Brett
12/3/2024 12:27:58 pm
It may not make a big difference for one dwelling unit, but when a building has the dwelling unit inside it hundreds of times then it makes a difference. Also, if a contractor sprinklers thousands of dwelling units per year it would be a significant cost to add sprinklers to rooms that don't require them.
Reply
Todd E Wyatt
12/3/2024 03:35:13 pm
Per IBC-2024 903.3.1.1.2, an automatic sprinkler system (ASPS) designed to NFPA 13 (not NFPA 13R) is exempt in Group R occupancies in "bathrooms" 55 SF or less that are in Dwelling Units or Sleeping Units provided the wall are of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating.
Reply