MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

OK to Leave Non-Required Sprinklers in Place?

10/5/2022

14 Comments

 
Can existing sprinkler heads that are no longer provide a code required purpose remain in place if the situation changes back in the future?

Situation #1:
A mall tenant space that is non-combustible construction with sprinklers at the deck, then a ceiling is added with pendents for new tenant.

Can the uprights remain in place for the likelihood of a future tenant that removes the drop ceiling and pendents?

Situation #2:
A nursing home dwelling unit closet with doors that had a pendent sprinkler.

Now doors are removed and a built in shelving unit was installed with just a 3-inch gap between the top of the unit and the head.

Can the head remain in place even though its not technically needed, for a time in the future when the shelfing unit may be removed and the space turned back to a closet?

Currently a customer is being cited by the state saying this situation needs to be corrected.

Would the heads all have to be removed?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Dan Wilder
10/5/2022 08:10:33 am

As a general rule, if it does not work as intended it needs to be removed (sound like this is not the case, but as you bring up the mall issue).

IFC 901.4.5 "Appearance of Equipment" - Any device that has the physical appearance of life safety or fire protection equipment but does not perform that life safety or fire protection function shall be removed. (this is geared more toward things like cameras but I have had inspectors use it for abandoned or non-functioning fire protection equipment)

NFPA 13-2022 Ed 30.2.2 - Where all or part of an inactive sprinkler system is abandoned in place, components including sprinklers, hose valves and hosed, and alarm devices shall be removed.

As to your questions:
#1 - Yes, acceptable to leave as they are still part of an active system just not a requirement.

#2 - If the space required sprinkler previously, the addition of solid shelving may need to be reviewed. Section 9.2.5.2 only allow the omission in hospital rooms, with the annex section specific to nursing homes/limited care facilities closets still requiring protection. Section 9.2.9 does allow removal of the sprinklers for "Furniture & Cabinets" as long as the sprinkler in the room covers to the wall behind the furniture (9.2.9.3 - this is new FYI).

Are you arguing for or against removing them?

On face value, I would say no protection required IF the sprinkler in the room covers the floor space of the new furniture (already have precedent in NFPA for that omission with trophy cases/wardrobes, and similar furniture). If not (I picture this closet having a pendent within and a sidewall above so the space would not be covered with the removal of the pendent sprinkler), the sprinkler needs to stay and the wardrobe modified for sprinkler clearance (the top removed).

Tough "What-If" but if you stick to NFPA and this was new (IMO), without the compliance of coverage area it's not us that needs the modification, the furniture guys need make adjustments.

Reply
David Kendrick
10/5/2022 08:11:02 am

Situation #2

From your description the 3" gap exceeds the 1" clearance required however you may find the authority deems them inaccessible for service as well as unworkable.

Speak to the customer and with permission ask the inspecting authority your question. Perhaps you can negotiate leaving the heads in place.

This is a liability business. Document, document, document.

Reply
Adam
10/5/2022 08:11:45 am

From a logic standpoint, as long as code requirements, such as minimum separation distances are met, and it can be shown that the system is still able to perform as intended hydraulically, I would think it's okay to exceed the code.

For the retirement home one, though, I would think that the shelving unit would impede the sprinkler pattern to such an extent that having this sprinkler go off would be a detriment to the system, since flow and pressure would be reduced to the other heads. Does the next closest head provide coverage to the shelving unit?

Could the sprinkler heads be removed, and the pipe outlets capped? This way it would be a simple solution to implement, and the heads may be reinstalled if a change were to take place.

Reply
franck
10/5/2022 08:21:31 am

If you keep them, you need to maintain them the same way as for required sprinklers

A possible way to remove the sprinklers with a possible quick return to service could be to remove sprinklers and replace with plugs

Still need to maintain sufficient heating for wet systems

Reply
Greg
10/5/2022 08:25:57 am

Situation 1: NFPA 25 would require visual inspection (of the sprinkler head) and that seems negated by the presence of a ceiling.

Acceptable heating (i.e. maintaining above 40F) may change when the drop ceiling is installed.

There may be more opportunity for leaks as the office space modification will likely require the system to be turned off, and when returning to service air pockets may occur in the deck-level sprinkler branch lines

False alarms may occur after the modification if the air is not vented by the sprinkler fitter.

If leaks occur on the tile and the tile becomes saturated, falls and causes injury or damage to the tenant space. Who is at fault? Is this a faulty design? And can liability be assessed against the sprinkler vendor's liability insurance for injuries and/or damage. After all, it was the sprinkler vendor who decided to leave the old piping in place, Right? (says the plaintiff's Lawer)

Repairing a leak (or cold weather break) will be complicated and require multiple trades to tear out the tiles, scaffold or lift up to the deck-level branch lines, and then re-tile, patch and paint.

Reply
Glenn Berger
10/5/2022 09:05:47 am

Good discussion items were mentioned above. If the sprinklers are active and maintained keep them in service. The sprinkles do present an additional level of fire protection that is not code required.

You do need to maintain documentation to describe the condition to any inspector or similar personnel that sees the facility.

Reply
Casey Milhorn
10/5/2022 09:23:12 am

It's a grey area (on purpose I believe) in the standards. I think it comes down to an owner's choice (that is if the AHJ doesn't have any input). The liability of leaving it in vs taking it out can go either way. What if you make the call, plug the heads, then have a leak at a plug? What if you make the call to leave it in, and it leaks? What if you take it out and there is a fire above ceiling? I always go back to car analogies. If a North Canadian bought a car from Florida with A/C on it, it's their choice whether to leave it on the car or not. They might not ever need it, but it's there if they do. Yes, they have the cost of maintaining it, but also the cost of taking it out, and then replacing it if they ever moved to a hot place. Either way it's their call and their consequences. It's not a perfect analogy, but helps us remember these buildings have owners that are responsible for their own buildings.

Reply
Tammi Worrell
10/5/2022 10:12:11 am

I'm a State Life Safety Code Surveyor. NFPA 101 says that even if a feature is not required, that feature must be maintained or removed.

4.6.12.3* Existing life safety features obvious to the public, if not required by the Code, shall be either maintained or removed.

Reply
Randy Kimbro
10/5/2022 10:23:53 am

As an AHJ, and respectfully to Dan's comments, "IFC 901.4.5 "Appearance of Equipment" - Any device that has the physical appearance of life safety or fire protection equipment but does not perform that life safety or fire protection function shall be removed. (this is geared more toward things like cameras but I have had inspectors use it for abandoned or non-functioning fire protection equipment)"

This IFC section is not about cameras but more about fire alarms and sprinklers in our opinion.

Per Greg's comment, "NFPA 25 would require visual inspection (of the sprinkler head) and that seems negated by the presence of a ceiling.". .... Annual sprinkler inspections are only required from ground level. Heads above a drop ceiling (unfortunately) never get inspected after installation.

If it is place, it must be maintained per IFC 901. The explanation is that a tenant (and perhaps insurance company) may erroneously rely on the safety of that fire protection thinking that it is still operational. We require any non-operational fire protection equipment to be removed.

As for Situation #1 with the mall tenant, I would have no problem leaving the sprinkler heads and uprights in place if they are operational and tested annually. I also see no problem with removing unneeded heads and plugging the pipes. Leaks can occur at anytime, so I have no concern there. They are identified and repaired as a normal course of operation.

Reply
Jesse
10/5/2022 10:25:35 am

If the system is active, and it sounds as if it is, you can leave the uprights in place.

The visualizing requirement in 25 is not applicable for sprinklers above a ceiling or in interstitial space.

Reply
DS
10/5/2022 11:58:22 am

Situation #1.
How would the installation of a ceiling not require the relocation of the uprights heads to pendants?

What would allow the omittance of sprinkler coverage?

Does the owner insure the building as a completely sprinklered building?

Situation #2
It is easy to determine if a sprinkler head can be omitted from a closet that is filled with millwork to create a built-in shelving system.

The code supports the omittance of sprinkler coverage in closets, but I don't see the support for situation #1.

Reply
Cliff Schulze
10/5/2022 02:16:15 pm

The one issue I don't see anyone talking about is the temperature of the heads above the ceiling of the mall tenant space. NFPA says that "sprinklers in an unventilated, concealed space, under an uninsulated roof, or in an unventilated attic shall be of the intermediate temperature classification."

Reply
Brian Cockburn
10/5/2022 04:06:42 pm

#1 - The existing sprinklers can remain. They are not required, but there's no harm in keeping them.

#2 - A shelf within 3" of an existing sprinkler might be a problem, but closets are such small spaces that if a sprinkler activates it seems impossible for them to not be flooded with water.

Aside: it's a good idea for sprinklers in closets to have wire guard cages installed. If someone puts something on the top shelf it could easily hit the sprinkler too hard and activate it.

Reply
Chris
10/6/2022 03:18:27 pm

Situation #1 Leaving them is no factor if they are still supplied with water. There are big concrete tilt panel buildings all over Houston with the heads still installed at the deck even though they built an office space inside the building with acoustic ceilings installed down below. A plug installed in the branch line outlet is just as likely to leak as the head that is already there so no factor there either.

Situation #2 I think I would demo it or install a cage on it.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top June '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT