Is there an NFPA 13 or 14 restriction for a combined sprinkler - standpipe dry system?
This is an open parking structure. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
12/5/2025 08:15:20 am
Definitely not a preferred method but if you can comply with NFPA 13 & 14 & get the AHJ buy-in, nothing directly prevents it that I am reading (mostly annex materials and interpretations) ....
Reply
Helena Vrettou
12/5/2025 08:38:18 am
There are worse in this project. The Fore Hoses are connected simply, on the feed pipes not the sprigs (thank God) but simply on the sprinklers pipes like a normal hose bib.
Reply
Brett
12/5/2025 09:00:15 am
Helena,
Reply
Pete H
12/5/2025 09:12:54 am
Can you FOIL the original design plans to see if this was submitted to an AHJ or if this was just installed wild wild west style?
Reply
Anthony
12/5/2025 08:47:35 am
I do not recommend this. Get a 'hot room' in a convenient location and run a dry system out from there. The delivery times with those larger pipes needed for standpipe flow will substantially slow down your delivery time.
Reply
Glenn Berger
12/5/2025 09:05:03 am
Are you trying to combine an Automatic Dry Pipe Sprinkler System with a Automatic Class I Dry Standpipe System????
Reply
Jesse
12/5/2025 09:10:59 am
Combined wet AS and SP systems are not uncommon at all. While I can't see a code reason that says no, I wouldn't recommend this for a bunch of reasons
Reply
Jack G
12/5/2025 11:06:18 am
If this is a nfpa 14 combined system and follows the rules, then yes.
Reply
Pete H
12/5/2025 12:09:54 pm
Really this does lead us to the question:
Reply